In the past when I wired RTU disconnects, I installed a 1/2 offset nipple out of the bottom to a bell box for my GFI outlet. Never failed an inspection for doing that. I haven't installed the disconnects yet, but I had a state inspector tell me today I am not allowed to do it that way.
The RTU disconnects are being fed with (2) #4 thhn, (1) #8 thhn GND & (2) #12 thhn for the GFI outlet, the #12's are/would be feeding through the disconnect to the GFI outlet.
I need a code reference for this, either allowed or not allowed.
Sorry my code book is at the job site & I haven't had a chance to look it up.
Thanks in advance for the help.:smile: