fire pump ats - control wiring

Status
Not open for further replies.

anbm

Senior Member
The control wiring from fire pump ats/controller to fire pump motor need to be installed in metal conduit? Thanks!
 

RUWired

Senior Member
Location
Pa.
The control wiring from fire pump ats/controller to fire pump motor need to be installed in metal conduit? Thanks!

anbm, article 695.6(E) states that all wiring from the controller to the pump motor shall be rigid metal conduit,intermediate, liquidtight metal or liquidtight non metallic and also listed mc and mi cables.

Rick
 

RUWired

Senior Member
Location
Pa.
I assume this rules doesn't apply for low voltage control wiring?

(E) Electric Fire Pump Control Wiring Methods. All electric motor?driven fire pump control wiring shall be in rigid metal conduit, intermediate metal conduit, liquidtight flexible metal conduit, liquidtight flexible nonmetallic conduit Type B (LFNC-B), listed Type MC cable with an impervious covering, or Type MI cable.

Rick
 