Thread: Ground Ring

  1. #1
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    7,436

    Ground Ring

    A ground ring per 250.52(A)(4) [encircle the building, min 2 awg] is commonly called out at telecommuncations sites, etc.
    Whats the theory behind a ground ring?
    Moderator-Washington State
    Ancora Imparo

  2. #2
    Join Date
    Feb 2003
    Location
    Florida
    Posts
    7,637
    Other than providing a convenient means of connecting equipment to the electrode system where multiple systems enter a building, and perhaps providing lower ground resistance than a few of the other approved electrodes, they are only as effective as any other electrode.

    For some applications, they can act as a counterpoise.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards

  3. #3
    Join Date
    May 2006
    Location
    USA
    Posts
    16
    Hello Tom
    A ground ring is an abbreviated form of what power companies and others call a grounding network or "grounding grid"
    Its benefits are many and the reasons to install them are numerous and some aspects are complex. I'll try to hit the high points.

    1. A ring provides a common point for all other grounding conductors to tie to. IF the ring and its attached components are of a sufficient size, then during a major electrical fault or even a lightning strike, all attached equipment rises to the same potential. If there is no difference in potential between the equiptment in one panel and the panel next to it, then no current will flow between those two devices and the risk of damage is minimal.

    2. Single point grounding is a common method of avoiding "loops" or parallel grounding paths in things electronic in nature. Looped ground paths are a nightmare and can be a personnel hazard. The large grounding ring (again, IF it is of sufficient size and capacity) provides for the common tie point and helps to avoid the dredded "loops".

    3 In lightning protection systems, the more copper conductor, ground rods, and real estate you have involved in your system, the more likely you are to survive a major lightning strike.
    Here in the Midwest, to effectively dissipate the energy of a lightning hit,
    we commonly use thousands of feet of 4/0 copper conductor buried to various depths.(depends on the engineers preference) Also many dozens of ground rods. (usually 3/4 X 10 ft) Several thousand square feet of land area is utilized to construct a "grid" so the those BILLIONS of watts of energy can be safely dissipated into the earth.

    That is why I referred to the "ring" as an abbreviated ground network.
    Mind you, a ring is much, much better than just a couple of ground rods sunk 6-8 ft. apart, but much better systems can be constructed that will safely handle some god-awful lightning shots.

    Well, that is just a drop in the ocean when it comes to grounding. I could go on, but I'll spare you.
    Hope this helps
    Regards
    Mike
    Electrical Safety is no Accident.
    Learn Not to Burn.

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    14,516
    Quote Originally Posted by subtech
    2. Single point grounding is a common method of avoiding "loops" or parallel grounding paths in things electronic in nature. Looped ground paths are a nightmare and can be a personnel hazard. The large grounding ring (again, IF it is of sufficient size and capacity) provides for the common tie point and helps to avoid the dredded "loops".
    I am curious. Please explain to me how parallel grounding paths can cause a personnel hazard, or for that matter create any kind of nightmare.

    Parallel ground paths are inevitable and cannot be eliminated. Think about large factories with metal piping systems and steel structures and rebar in the concrete all over the place. A ground ring just makes this situation "worse".

    What is a hazard is when the neutral leg of a power system is grounded at more than one point, causing current flow on the EGC. The ground ring does absolutely nothing to solve that problem.
    Bob

  5. #5
    Join Date
    May 2006
    Location
    USA
    Posts
    16
    Hello petersonra

    Okay, here goes.
    In substations where I do most of my work, parallel and multiple ground paths in current transformer ckts. that are connected to protective relays are a scourge. Recently, while I was working on control wiring problem in a substation, a 13 kv feeder that originated in this same sub experienced a hard ground fault. Because the neutral conductors in several ct ckts had been connected to earth ground in multilple locations, a portion of the ground fault return current appeared in the neutrals of these ct circuits.(these neutrals were in effect "in parallel" with the grounding grid) This resulted in a breaker failure relay operation at the 161kv level which dumped part of a large substation. Half of the 13 kv switchgear was also lost due to a differential operation which caused loss of auxilliary operations in a nearby power plant. Two units were taken off line as well as the plant itself going partially dark. In the resulting scramble to find out just what happened, one plant electrician was injured in a fall. All of this from one or two "mis-applied" grounding jumpers.
    Another incident involving Pt's and a metering circuit resulted in some damaged digital revenue metering equipment.
    Most all literature dealing with protective relays, metering equipment, communications gear warn against multiple and parallel earth connections.
    Also, in the electricians or wireman's world, doesn't the NEC mandate that there will only be 1 earth ground connected in a main panel entrance? (I'm not an electrician so my code knowledge is very limited)
    I can go on about a substation tech friend of mine who was working on a corner grounded delta secondary and found out the hard way that it was grounded in more than one location(same corner of the delta, different earth ground jumper).
    Then there was the flash fried aluminum relay rack that turned out to be in series with a large paralleled run of 4/0 ground grid conductor that turned out to be a favored path of return current for a 69-13 kv 30 MVA power transfomer. The run of 4/0 turned out to be one of only two surving runs left to the X0 bushing after some digging was done in the area.
    Then, there was the time...........................
    Okay, I'm getting carried away. However, parallel grounding paths placed in the wrong places can cause all kinds of problems and end up getting un-suspecting workers injured. Unfortunately, I've seen it. If you require any more proof of this, I'll be glad to converse with via email. Let me know.
    Regards
    Electrical Safety is no Accident.
    Learn Not to Burn.

  6. #6
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    14,516
    I noticed in your missive you stated that a neutral wire was grounded in two points. That is generally prohibited because you end up with current flow on the EGC. I mentioned in my previous post that this is a big no-no.

    There is nothing inherently wrong with grounding in parallel, as long as the neutral wire is connected at only one point.
    Bob

  7. #7
    Join Date
    May 2006
    Location
    USA
    Posts
    16
    Oh, by the way, when part of the current that should flow back to the panel in the neutral conductor flows back in the EGC..........uh, doesn't that result in a gfci breaker trip? Thought so.

    Regards
    Electrical Safety is no Accident.
    Learn Not to Burn.

  8. #8
    Join Date
    Nov 2004
    Location
    Las Cruces N.M.
    Posts
    1,092
    Quote by subtech
    "In substations where I do most of my work, parallel and multiple ground paths in current transformer ckts. that are connected to protective relays are a scourge"

    While I agree that instrumentation doesn't always operate well with multiple grounds, utility systems generally operate with thousands of grounds, each causing the "dreaded loop". There is no inherent danger in multiple grounds if properly installed, utilities do it every day.

    second quote
    "uh, doesn't that result in a gfci breaker trip? Thought so."

    Only if there is a gfci breaker or receptacle.

    Jim T

  9. #9
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    2,866
    Hmm. Keep in mind that the _rules_ for power distribution systems are rather different than the NEC _rules_.

    Multiple earthing of distribution systems is the norm, and this most certainly does result in 'parallel' current flow through the earth.

    I presume that subtech is talking about multiple metallic paths between grounded elements of the system.

    Any connection between the grounded conductor system and other conductive materials will result in a parallel path, which can either result in nusiance tripping _or_ desensitization of ground fault detection equipment, depending upon the particular hardware involved.

    Back to grounding rings: I've wondered if a grounding ring would act as an 'equipotential shell' to some extent, not only providing the necessary grounding electrode, but also 'shunting' any earth currents around the encircled structure.

    -Jon

  10. #10
    Join Date
    Dec 2005
    Location
    tampa florida
    Posts
    46

    Grounding rings in data centers

    in a perfect system all current flows on the neutral, none on the EGC, the N-G voltage is minimal and G voltage is the same everywhere. However, in data centers 1. the best equipment isn't always used 2. power supplies can leak a little current to ground. 3. there are many seperately derived systems (UPS and xfmr) and 4. AC and DC power is used through out the floor. All these components can change the G voltage to earth in different areas of a data center. the idea of a grounding ring or grounding grid as some use is to provide a low impedance path for all the equipment in the center to connect. The data lines which connect all these pieces of equipment also have a ground in them, and some a shield. having a low resistance parallel path helps prevent data loss due to G voltage inconsistancies. I guess i thought of the grounding ring as a means to level the ground voltage gradient in different portions of a large area.