    In-use covers

    Let's not get into local issues, just the NEC. On a new single family dwelling, are in-use covers required on all exterior receptacles? If so Code article numbers would be great. Thanks have a great day.

  2. #2
    Join Date
    Dec 2004
    Location
    North Carolina
    Posts
    4,446
    Read 406.8
    Mike Whitt
    God answers Knee-Mail.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,256
    Quote Originally Posted by dad
    Let's not get into local issues, just the NEC. On a new single family dwelling, are in-use covers required on all exterior receptacles? If so Code article numbers would be great. Thanks have a great day.

    They are only required on a receptacle in wet locations. A hinged type cover can be used in damp locations.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  4. #4
    Join Date
    Dec 2004
    Location
    Fort Collins, CO NEC: 2014
    Posts
    15,472
    Due to varied interpretations of "protected from the weather", I have taken to installing in-use covers in all locations outside. Just my preference.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,256
    Quote Originally Posted by georgestolz
    Due to varied interpretations of "protected from the weather", I have taken to installing in-use covers in all locations outside. Just my preference.

    Would your customers be happy with a big bubble cover hanging on the underside of their outdoor soffits? Mine would scream if they had to look at those ugly covers hanging there.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  6. #6
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    21,838
    We typically use a 45-degree angle for wind-blown rain in determining the wet/damp issue. In other words, if the receptacle is 7' below the roof edge, it needs to be at least 7' under the protecting roof/eave, etc. to avoid the bubble.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #7
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    2,439
    Quote Originally Posted by infinity
    Would your customers be happy with a big bubble cover hanging on the underside of their outdoor soffits? Mine would scream if they had to look at those ugly covers hanging there.
    And herein lies the problem !!! Your AHJ and the NEC may require you to install those bubble covers but I can guarantee you that those will quickly change to the flip cover after the inspection process (either by an electrician or by the homeowner). Manufacturers (like Intermatic) are touting slogans on their products that indicate "It's the Code" but I'd be willing to bet that none of them live in a mega-mansion that took a $million or so to build.

    My opinion, either re-write the code to include only those receptacles that have a definite use and have a cord plugged in at all times or compel the manufacturers to come up with a product that isn't so obtrusive and that can be easily attached to an outdoor receptacle by a homeowner.

    Just my opinion. Not looking to become part of the CMP !!!

  8. #8
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,024
    Phil I doubt this is what you meant but it sounds like your saying there should be a separate set of rules for folks who have mega-mansions that took a $million or so to build.

    How about this, they pay a little more for the carpenters to build a cubby hole in the wall to hide the outlet or have the electrician use a recessed box like the one Arlington sells?

    http://www.aifittings.com/whnew74.htm


  9. #9
    Join Date
    Dec 2004
    Location
    Fort Collins, CO NEC: 2014
    Posts
    15,472
    Quote Originally Posted by infinity
    Would your customers be happy with a big bubble cover hanging on the underside of their outdoor soffits? Mine would scream if they had to look at those ugly covers hanging there.
    No, that is an exception. I use damp covers for the soffits.

  10. #10
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,256
    Quote Originally Posted by georgestolz
    No, that is an exception. I use damp covers for the soffits.

    We do also. I was saying that in response to the OP question that all exterior receptacles do not require so called in-use covers.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted