    Permiited location for fire alarm control panel

    Does anyone know if it is permissable or not to locate a fire alarm control panel in a fire pump room?

  2. #2
    Join Date
    Nov 2004
    Location
    Las Cruces N.M.
    Posts
    1,089
    That is almost always a question for the AHJ. I recently had an inspector insist that a panel be mounted on the wall across from the secretary's desk. That way it would be monitored. On the other hand, a sprinkler monitoring panel was allowed to be mounted in the sprinkler riser room.

    Jim T

  3. #3
    Join Date
    Aug 2006
    Location
    Yakima, Washington
    Posts
    2

    Location

    In the past year, we have installed 9 fire pumps and controllers, in 5 different jurisdictions. We could mount the FACP in the control room or in other locations appropriate for the panel.
    When you submit to the local AHJ, point out the FACP in the pump control room. If he has a problem with it, he will likely point it out to you.

    good luck

  4. #4
    Join Date
    Oct 2006
    Location
    Portland, OR
    Posts
    15
    It depends on the AHJ. An FACP installed in a fire pump room is a potential service call. Its only a matter of time when it gets wet.. ehehehehe
    Nothing right in my left brain,
    nothing left in my right brain.
    'Ever since then I've seen the past in one eye and the present in the other'

  5. #5
    Join Date
    Sep 2003
    Posts
    333
    In my humble experience, the Fire Dept wants to see what's going on immediately upon entering the building during an alarm. The FACP can be located almost anywhere, IF you put a remote annunciator near the building main entrance.

  6. #6
    Join Date
    Jul 2006
    Location
    Cape Coral, Fl.
    Posts
    299
    Make sure the space has a temperature control (HVAC/heat). If the space doesn't, then you will have to bring in conditioned air to the FACP. I have several installations with a FACP in a 1' foot deep , 3' foot wide room with flex duct serving it for temp control on the FACP.
    Living in the sunshine, staying contented most of the time.