Thread: High Voltage Transformer Feeder

  1. #1
    Join Date
    Jun 2003
    Posts
    5,559

    High Voltage Transformer Feeder

    OK, I'm specifying a 12KV feeder for a 2500KVA transformer. I was wondering if this sounds like the right way to go:

    2500KVA/12KV/sqrt(3) *1.25 = 150 amps primary OCP. So I would use #2 copper XLP based on table 310.77. (I never know if this table applies to 3 conductors in a single burried conduit).

    From the notes on table 310.64, I would assume it would be safe to use 133% although I'm not sure if the loop I am taking power from is grounded or not.

    From Southwire, I got a cut sheet on their XLP cable:

    http://appprod.southwire.com/Product...rodcatsheet105

    It looks like #2 has about a 1" diameter. Thats 0.79 square inches. If I put 3 of these into a single conduit, I need 2.4% of conduit area at 40% fill. So it looks like a 3" conduit will work (see edit below).

    Or would it be better to install one cable in each of 3 conduits? Can I do that with metal conduit, or would that have to be PVC?

    A couple of more questions: Whats the difference between XLP and EPR? Would one be better for this than the other? How about the difference between "Tape" and "Wire" sheilds?

    Steve

    Edit:

    I already see that jambing might be a problem, so it looks like it is 4" conduit.
    Last edited by steve66; 08-23-06 at 05:56 PM.

  2. #2
    Join Date
    Nov 2004
    Location
    Las Cruces N.M.
    Posts
    1,086
    Quote Originally Posted by steve66
    It looks like #2 has about a 1" diameter. Thats 0.79 square inches. If I put 3 of these into a single conduit, I need 2.4% of conduit area at 40% fill. So it looks like a 3" conduit will work (see edit below).

    Or would it be better to install one cable in each of 3 conduits? Can I do that with metal conduit, or would that have to be PVC?

    A couple of more questions: Whats the difference between XLP and EPR? Would one be better for this than the other? How about the difference between "Tape" and "Wire" sheilds?

    Steve

    Edit:

    I already see that jambing might be a problem, so it looks like it is 4" conduit.
    Steve I think you'd be happy with 4", but you are performing the right calculations. I prefer one conduit for all cables, including neutral/ground, but a local utility in our area uses 3 conduits with a hot wire and neutral/ground in each. I specify wire shield over tape shield, but don't have a problem with either.

    XLP insluation, cross linked polyethylene, is a bit older and often times considered somewhat less reliable than EPR. EPR, ethylene propylene rubber, is only slightly newer, and is considered by many to be more reilable. That will often incite an argument but I agree with it.

    Be sure to determine grounding, and the need for a neutral. Often times padmounted transformers are wye-wye vs delta-wye and in the first type you must have a neutral.

    Jim T

  3. #3
    Join Date
    Feb 2003
    Location
    Alabama
    Posts
    2,549
    Utilities here will install all cables in one conduit and a spare conduit.

  4. #4
    Join Date
    Jun 2003
    Posts
    5,559
    All cables in one conduit with a spare sounds like a plan

    I see there is also TRXLP:

    http://appprod.southwire.com/Product...prodcatsheet52

    And I have also seen XLPE cable. Does anyone know where I can find out what the differences are?

    Steve

  5. #5
    Join Date
    Nov 2004
    Location
    Las Cruces N.M.
    Posts
    1,086
    XLP and XLPE are thse same, cross linked polyethylene. The TRXLPE is tree retardant cross linked poly. A common mode of failure in XLPE cables in slow degredation of the insulation. It actually grows little tree like structures from the conductor, thru the insulation towards the ground. After a while the insulation has broken down enough to fault. When you disect the cable you can see little dendritic "trees" under a micorscope.

    The TRXLPE is treated to inhibit the growth of these trees.

    There should be a lot of info available thru a google search.

    Jim T

  6. #6
    Join Date
    Aug 2006
    Location
    Red_neck_vill USA
    Posts
    5

    hope this helps

    This is a web site I used to figure out the diffrence in cable insulation just download the pdf file and look towads the last few pages it will show what the insulation is sutiable for.

    http://web.anixter.com/Anixter/anixt...acketMaterials

  7. #7
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,183
    Medium voltage devices and equipment are all 100% rated. No need to increase the cable by the 125% like is done with lower voltage systems (480V power circuit breakers are also 100% rated) Therefore, the current is 121 A. This does not necessarily affect the cable size, because for 15kV voltage class, #2AWG is typically the smallest cable manufactured. As you probably saw from the Southwire catalog.

    Keep in mind, that Southwire, like others, do not manufacture a MV-90 cable anymore. They have standardized on MV-105. So the current ratings you see in their catalog are for 105 deg C, not 90 deg C.

    As far as 310.77, unless your going to put concrete around the conduit, then technically, it does not apply. This is because it is usual and customary to put concrete around MV Conduit.

    EPR is more flexible, however not quite as durable as XLPE. The PVC jacket will help protect the insulation during pulling.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  8. #8
    Join Date
    Jun 2003
    Posts
    5,559
    I didn't know what they meant by tree retardant. I wonder if that is a problem even if the cable is never overdriven, or completely heated up.

    Thanks for the link C_CLEV. That does give the differences between XLP and EPR. Right now I'm thinking the TRXLP will work.

    Kingpb:

    Southwires cut sheet specifically says 90 deg. under normal conditions, although their ampacities do seem to be higher than in the NEC tables. I still want the primary OCP on the transformer to be 125% the full load current, so thats why I applied 125%.

    You say it is usual and customary to put concrete around MV Conduit. Does that mean it would be unusual to not concrete encase it??? Some of this run may be horiz. bored.

    Steve

  9. #9
    Join Date
    Nov 2004
    Location
    Las Cruces N.M.
    Posts
    1,086
    Steve

    The trees are believed to originate from overvoltages not overloads. Lightning arresters, etc., can limit the energy into an underground system, but a voltage wave will still be past thru the riser and into the ug system. In my experience the tree retardant XLP is supposed to limit the insulation degredation from this overvoltage. I believe it is as much hype as it is effective, but probably helps a bit.

    90C is as standard rating because the connectors, elbows, etc., are generally rated 90C.

    Jim T

  10. #10
    Join Date
    Feb 2003
    Location
    Alabama
    Posts
    2,549
    Quote Originally Posted by kingpb
    As far as 310.77, unless your going to put concrete around the conduit, then technically, it does not apply. This is because it is usual and customary to put concrete around MV Conduit.
    I am assuming that the this is a riser that that taps the utility 12 kv feeder
    and cable runs from the pole to the transformer. I don't think its necessary to
    install the conduit in concrete if it is installed in accordance with table
    300.50. I would use PVC sch 80. I would use 36" as the min depth just for added safety.

    Quote Originally Posted by Steve
    OK, I'm specifying a 12KV feeder for a 2500KVA transformer. From the notes on table 310.64, I would assume it would be safe to use 133% although I'm not sure if the loop I am taking power from is grounded or not.
    The notation 12kv is likely a 12.46 kv wye system with the neutral grounded.
    Last edited by bob; 08-24-06 at 02:57 PM.