Question PVC in Plenum
I over heard a discussion regarding the use of PVC above a Plenum ceiling. It was basically stated that because the suspended ceiling was used as a “return” the PVC would not be Code compliant.
I am looking in article 352 but can not find the discrepancy. Perhaps it is in the building Code?
Any comments would be appreciated.
Justin J. Walecka
__________________
Posts are my opinion only
  #2
Old 08-29-2006, 07:17 PM
RUWired RUWired is offline
Default
Justin, Article 300.22(B) explains the wiring methods allowed, and pvc is not listed
(B) Ducts or Plenums Used for Environmental Air Only wiring methods consisting of Type MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these ducts and plenum chambers. The connectors used with flexible metal conduit shall effectively close any openings in the connection. Equipment and devices shall be permitted within such ducts or plenum chambers only if necessary for their direct action upon, or sensing of, the contained air. Where equipment or devices are installed and illumination is necessary to facilitate maintenance and repair, enclosed gasketed-type luminaires (fixtures) shall be permitted.
Rick
  #3
Old 08-29-2006, 07:25 PM
Default
300.22(C) also covers plenums above suspended ceilings
FPN: The space over a hung ceiling used for environmental air-handling purposes is an example of the type of other space to which this section applies.
Rick
  #4
Old 08-29-2006, 08:58 PM
cpal cpal is offline
Default
Justin
300.22 (C) is titled as "Other Space Used for Environmental Air."
I would explain this as a suspended ceiling where enviormental air is generally returned through a egg crate type tile(s) to the mechanical unit. This type of installation is not a plenumn.
ref to the definition in art 100.
That being said it appears that the general rule would not permit a PVC jacket in such locations this section is stricter for sections 300.22(A) and (B)
Charlie
  #5
Old 08-29-2006, 09:03 PM
marcb marcb is offline
Banned
Default
No shirt, no shoes, pvc located in a plenum....no dice
  #6
Old 08-30-2006, 07:06 AM
iwire's Avatar
iwire iwire is offline
Default
It's not a plenum to the NEC.
__________________
Bob
  #7
Old 08-30-2006, 08:42 PM
JJWalecka's Avatar
Default
Rick, Charlie, Marcb and Iwire thank you for your time and effort.
I should have done more research before asking the question.
Justin J. Walecka
__________________
  #8
Old 08-30-2006, 10:23 PM
ryan_618's Avatar
ryan_618 ryan_618 is offline
Default
Quote:
Actually, it would be in the mechanical code, such as the IMC. Anything in an air handling space must have a certain flame spread and smoke developed index.
__________________
Ryan Jackson, Salt Lake City
Inspector, Instructor
  #9
Old 08-31-2006, 08:06 PM
JJWalecka's Avatar
Default
Ryan,
Thank you!
Justin J. Walecka
__________________
Closed Thread
Motor Controls Forums
Search this Thread:
Advanced Search
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
- Archive - Top
Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.