I over heard a discussion regarding the use of PVC above a Plenum ceiling. It was basically stated that because the suspended ceiling was used as a “return” the PVC would not be Code compliant.
I am looking in article 352 but can not find the discrepancy. Perhaps it is in the building Code?
Any comments would be appreciated.

Justin J. Walecka
__________________
Posts are my opinion only.
  #2  
Old 08-29-2006, 06:17 PM
RUWired RUWired is offline
Senior Member
 
Join Date: Feb 2006
Location: Pa.
Posts: 1,780
Default

Justin, Article 300.22(B) explains the wiring methods allowed, and pvc is not listed

(B) Ducts or Plenums Used for Environmental Air Only wiring methods consisting of Type MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these ducts and plenum chambers. The connectors used with flexible metal conduit shall effectively close any openings in the connection. Equipment and devices shall be permitted within such ducts or plenum chambers only if necessary for their direct action upon, or sensing of, the contained air. Where equipment or devices are installed and illumination is necessary to facilitate maintenance and repair, enclosed gasketed-type luminaires (fixtures) shall be permitted.
Rick
  #3  
Old 08-29-2006, 06:25 PM
RUWired RUWired is offline
Senior Member
 
Join Date: Feb 2006
Location: Pa.
Posts: 1,780
Default

300.22(C) also covers plenums above suspended ceilings

FPN: The space over a hung ceiling used for environmental air-handling purposes is an example of the type of other space to which this section applies.
Rick
  #4  
Old 08-29-2006, 07:58 PM
cpal cpal is offline
Senior Member
 
Join Date: May 2004
Location: MA
Posts: 1,416
Default

Justin

300.22 (C) is titled as "Other Space Used for Environmental Air."

I would explain this as a suspended ceiling where enviormental air is generally returned through a egg crate type tile(s) to the mechanical unit. This type of installation is not a plenumn.

ref to the definition in art 100.

That being said it appears that the general rule would not permit a PVC jacket in such locations this section is stricter for sections 300.22(A) and (B)

Charlie
  #5  
Old 08-29-2006, 08:03 PM
marcb marcb is offline
Banned
 
Join Date: Jun 2006
Location: Roseville
Posts: 105
Default

No shirt, no shoes, pvc located in a plenum....no dice
  #6  
Old 08-30-2006, 06:06 AM
iwire's Avatar
iwire iwire is offline
Moderator
 
Join Date: Feb 2003
Location: Massachusetts
Posts: 37,441
Default

It's not a plenum to the NEC.
__________________
Bob
  #7  
Old 08-30-2006, 07:42 PM
JJWalecka's Avatar
JJWalecka JJWalecka is offline
Senior Member
 
Join Date: Feb 2005
Location: New England
Posts: 829
Default

Rick, Charlie, Marcb and Iwire thank you for your time and effort.

I should have done more research before asking the question.


Justin J. Walecka
__________________
Posts are my opinion only.
  #8  
Old 08-30-2006, 09:23 PM
ryan_618's Avatar
ryan_618 ryan_618 is offline
Moderator
 
Join Date: May 2003
Location: Salt Lake City, Utah
Posts: 5,284
Default

Quote:
Originally Posted by JJWalecka
Perhaps it is in the building Code?
Actually, it would be in the mechanical code, such as the IMC. Anything in an air handling space must have a certain flame spread and smoke developed index.
__________________
Ryan Jackson, Salt Lake City
Inspector, Instructor
  #9  
Old 08-31-2006, 07:06 PM
JJWalecka's Avatar
JJWalecka JJWalecka is offline
Senior Member
 
Join Date: Feb 2005
Location: New England
Posts: 829
Default

Ryan,

Thank you!


Justin J. Walecka
__________________
Posts are my opinion only.
Closed Thread

CEU Banner Home Page

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:23 PM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.