Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
I have 3 sync'ed 5KW inverters that put out 208/120 3ph. I need 480/277. Simple, just need a stepup transformer......But the 480 side feeds a remote Delta->Wye xfmr.

[When the inverters are not on-line, a PoCo xfmr feeds us from a wye. When Reddi Kilowatt goes on vacation, an ATS will switch from it to the inverters.]

I can't see any way around a Wye-Wye transformer, but know that brings a host of issues. Is there such a thing as Wye-Delta-Wye, or one with an aux. delta winding to control the harmonics?
 

ericsherman37

Senior Member
Location
Oregon Coast
Transformers aren't my forte, but can't you just feed the remote Delta transformer with 480 from your new step-up transformer? It doesn't need a neutral for its primary side, right? I don't see why it would care; 480 is 480.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The philosophical radio station: WYOY

I can't see any way around a Wye-Wye transformer, but know that brings a host of issues. Is there such a thing as Wye-Delta-Wye, or one with an aux. delta winding to control the harmonics?
A wye-primary transformer should be supplied as if it were a Delta primary. Just let the primary neutral (H0) float. You don't need to supply a primary neutral.
 

Smart $

Esteemed Member
Location
Ohio
I have 3 sync'ed 5KW inverters that put out 208/120 3ph. I need 480/277. Simple, just need a stepup transformer......But the 480 side feeds a remote Delta->Wye xfmr.

[When the inverters are not on-line, a PoCo xfmr feeds us from a wye. When Reddi Kilowatt goes on vacation, an ATS will switch from it to the inverters.]

I can't see any way around a Wye-Wye transformer, but know that brings a host of issues. Is there such a thing as Wye-Delta-Wye, or one with an aux. delta winding to control the harmonics?

What voltage is the remote delta-wye secondary? If 208Y/120, why not tie the inverters into its secondary? ...voltage drop issues?
 

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
What voltage is the remote delta-wye secondary? If 208Y/120, why not tie the inverters into its secondary? ...voltage drop issues?

It is 208Y/120.

The stepdown is 1100 ft away. Besides the stepdown, there are multiple 480 3ph motors there. We're at 480 to keep down the losses and costs down; even so, we're pulling 3*500 MCM, plus gnd & a neutral [in case a single phase 277 load emerges in the future...]

We could abandon that 277 possibility, but if we feed a delta primary with a delta source; then everything floats without constraint. I believe that is what's called "ill-advised".... {There's another issue that precludes such, which I'm skipping for now..}


[We priced out up-converting the Poco and inverter to 4160, and then down to 208Y; but it was $5K more with only slightly less loss, and the local electrician was sure the AHJ would have kittens over 4160 at a residence.]
 

ericsherman37

Senior Member
Location
Oregon Coast
A wye-primary transformer should be supplied as if it were a Delta primary. Just let the primary neutral (H0) float. You don't need to supply a primary neutral.

See, that's what makes sense to me. Wire the 208 primary for Delta and then the secondary could be your 480/277, and the remote transformer can just take a 480 3? feed from there.

Yah?
 

Smart $

Esteemed Member
Location
Ohio
It is 208Y/120.

The stepdown is 1100 ft away. Besides the stepdown, there are multiple 480 3ph motors there. We're at 480 to keep down the losses and costs down; even so, we're pulling 3*500 MCM, plus gnd & a neutral [in case a single phase 277 load emerges in the future...]

We could abandon that 277 possibility, but if we feed a delta primary with a delta source; then everything floats without constraint. I believe that is what's called "ill-advised".... {There's another issue that precludes such, which I'm skipping for now..}


[We priced out up-converting the Poco and inverter to 4160, and then down to 208Y; but it was $5K more with only slightly less loss, and the local electrician was sure the AHJ would have kittens over 4160 at a residence.]
Then a 208D to 480Y xfmr appears to be the best solution.
 

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
Then a 208D to 480Y xfmr appears to be the best solution.

To fill in some of the additional factors....

1) So the standby three inverters each have a L and a N output terminal. I tie the N's together. Does that 3*N then float....? [I'm having a hard time picturing this today (little sleep last night), so if it's obvious, I apologize.]

2) On the 480 side, there are grid-tie inverters that put out 277 L-N.
They support the downstream loads both in PoCo & standby modes; and if there is excess output, they'll backcharge the standby inverters' battery string through the transformer in question. A problem or not?
 

Smart $

Esteemed Member
Location
Ohio
To fill in some of the additional factors....

1) So the standby three inverters each have a L and a N output terminal. I tie the N's together. Does that 3*N then float....? [I'm having a hard time picturing this today (little sleep last night), so if it's obvious, I apologize.]

2) On the 480 side, there are grid-tie inverters that put out 277 L-N.
They support the downstream loads both in PoCo & standby modes; and if there is excess output, they'll backcharge the standby inverters' battery string through the transformer in question. A problem or not?
#1. N is required to be grounded.

#2. I don't see it as a problem.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
To fill in some of the additional factors....

1) So the standby three inverters each have a L and a N output terminal. I tie the N's together. Does that 3*N then float....? [I'm having a hard time picturing this today (little sleep last night), so if it's obvious, I apologize.]
Oh, I didn't realize you meant three 1-ph units being combined as a wye source. I envisioned three paralleled units.

I'd clear it with the manufacturer, but yes, join (and bond, if not already done) the inverter out N's together, but supply the transformer as a Delta load.

2) On the 480 side, there are grid-tie inverters that put out 277 L-N.
They support the downstream loads both in PoCo & standby modes; and if there is excess output, they'll backcharge the standby inverters' battery string through the transformer in question. A problem or not?
Hmmm. Now, we need to know if three wye-connected inverters can accept a Delta load as a recharging source. Again, the manufacturer should be consulted.
 

jghrist

Senior Member
To fill in some of the additional factors....

1) So the standby three inverters each have a L and a N output terminal. I tie the N's together. Does that 3*N then float....? [I'm having a hard time picturing this today (little sleep last night), so if it's obvious, I apologize.]
[When the inverters are not on-line, a PoCo xfmr feeds us from a wye. When Reddi Kilowatt goes on vacation, an ATS will switch from it to the inverters.]
When not on utility power, what keeps the three 1? inverter output voltages 120? apart?
 