Thread: voltage between neutral and ground

  1. #1
    Join Date
    Oct 2006
    Posts
    26

    voltage between neutral and ground

    I have supply source with 3-phase and neutral without ground to feed our telecommunication shelter through distribution panel.
    we made seperate earth and connected to the panel, and when i measured tha voltage between neutral and earth bar in the panel using DMM i found that it reads 10 volt.what is the reason for this voltage difference.

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    18,595
    Is the neutral bonded to earth at any point?
    Don
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  3. #3
    Join Date
    Jan 2004
    Location
    Right here.
    Posts
    12,326
    Sounds like "phantom voltage". Put your fingers on the DMM leads, and the votlage will likely go to -zero-.

  4. #4
    Join Date
    Sep 2006
    Location
    Atlantis
    Posts
    286
    "I have supply source with 3-phase and neutral without ground"

    Neutral is not grounded? Is that correct?

  5. #5
    Join Date
    Jan 2004
    Location
    Right here.
    Posts
    12,326
    Ahhh,.. they have a subpanel and they're trying to use the earth as the EGC. Oops... I missed that part. Yeah, that is certainly a potential difference. The voltage will go away when a N-G bonding is added or the 5th conductor run from the MDP.

  6. #6
    Join Date
    Oct 2006
    Posts
    26
    no connections between earth and neutral.

  7. #7
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    18,595
    If there are no connections between the electrical system and earth the system is floated and the voltage to ground can be any voltage between 0 and the system voltage.
    Don
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  8. #8
    Join Date
    Oct 2006
    Posts
    26
    The neutral is earthed from the supply side, but i measured voltage between it and my own earth at the panel.

  9. #9
    Join Date
    Aug 2004
    Posts
    10,944
    Quote Originally Posted by etalaat
    The neutral is earthed from the supply side, but i measured voltage between it and my own earth at the panel.
    what are you refering to when you say "earth"? A rod you sunk in the ground at the new panel or the green wire you ran with the feeder?
    Bob

  10. #10
    Join Date
    Feb 2003
    Location
    Plano, TX
    Posts
    3,741
    Etallat, I am a telecom power engineer and from what you describe not only violates code but is extremely dangerous to personnel and likely to cuase a great deal of noise and equipment malfunction.

    Sounds to me like you fell for the “MY EQUIPMENT NEEDS AN ISOLATED GROUND TRICK”. The panel used for your telecom panel has to have a ground (EGC) ran from the service panel. Sounds like you just added a rod which is floating and isolated from the building ground electrode system. That is why you are measuring a voltage. What you should see is something on the order of 1 or 2 volts between N-G at your telecom branch panel. That voltage of 1 or 2 volts is normal and is a result the I*R voltage drop developed on the neutral from load current.

    If you are wanting to establish a new reference point for the telecom panel, you went about it the wrong way. To do this you would need to install a separately derived transformer in the telecom electrical room to establish a new N-G bond and reference point. However, even doing this still requires you to use the buildings ground electrode system and not a isolated ground rod.