do metal luminares need a ground wire

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
When I look at 410-18 (a) Exposed conductive parts. ....
what are they reffering to when it's written " exposed metal parts shall be grounded or insulated from gorund...

Are they reffering to the conductors?
or are they referring to metal parts that could conduct?

Later code 401-20 and 410-21 talk about having a grounding conductor.

I would think that metal fixtures manufactured today need a grounding means.
 

Smart $

Esteemed Member
Location
Ohio
...

Are they reffering to the conductors?
or are they referring to metal parts that could conduct?

...
They are referring to exposed metal, i.e. that which is not intended to deliver power to equipment.

Metal housings of luminaire's are generally such exposed metal.
 