is there anywhere in the code book that says whether or not you can't or you can put a multiwire cirucit that feeds ONLY 120v loads on a 2pole breaker. i have looked and i can't find anything that says that you can't, but i can't find anything that says you can
luke
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
electricdrill said:
is there anywhere in the code book that says whether or not you can't or you can put a multiwire cirucit that feeds ONLY 120v loads on a 2pole breaker. i have looked and i can't find anything that says that you can't, but i can't find anything that says you can
luke

You can do it. It is not an issue.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Art. 210.4(B) of the 2008 will require simultaneously disconnect all ungrounded conducts for a multiwire branch circuit
 

paul

Senior Member
Location
Snohomish, WA
Dennis Alwon said:
Art. 210.4(B) of the 2008 will require simultaneously disconnect all ungrounded conducts for a multiwire branch circuit


BOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOOO!


:D
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
paul said:
You can put a single wire on a 3-pole breaker if you wish.

This is indeed correct but I think the op wanted to know if can use a double pole for a MWBC instead of 2 sp breakers.
 

paul

Senior Member
Location
Snohomish, WA
Dennis Alwon said:
This is indeed correct but I think the op wanted to know if can use a double pole for a MWBC instead of 2 sp breakers.

Yeah, I sorta reversed what he was asking. I guess my point is, at this time, it doesn't matter where you use 2pole or 3pole breakers...until 2008 of course.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Dennis Alwon said:
Art. 210.4(B) of the 2008 will require simultaneously disconnect all ungrounded conducts for a multiwire branch circuit

Now isnt that a great idea ? One circuit fails and we can kill every cubical at same time.And power poles have common neutral so i cant fix by giving each its own neutral.Let me guess,3pole breakers cost more.
 

dbuckley

Senior Member
In my opinion this requirement is well overdue.

Of course, if you dont like it, or the job calls for it, you can always run more neutrals, theres no requirement to actually use a MWBC. But if you do, starting with the 2008 book, you have to do them "properly".
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Jim,
Now isnt that a great idea ? One circuit fails and we can kill every cubical at same time.
The rule does not require common trip, only a means of common disconnect. The new code rule can be complied with by the use of a handle tie and many times when one of the breakers trips it does not turn the other one(s) off.
Don
 

tallguy

Senior Member
don_resqcapt19 said:
Jim,

The rule does not require common trip, only a means of common disconnect. The new code rule can be complied with by the use of a handle tie and many times when one of the breakers trips it does not turn the other one(s) off.
Don
Can one then legitmately temporarily remove the handle tie in order to reset the tripped breaker without turning off the other one??
 

iwire

Moderator
Staff member
Location
Massachusetts
dbuckley said:
But if you do, starting with the 2008 book, you have to do them "properly".

Hold on buddy, I have been doing them 'properly' for years most times with SP breakers.

The NEC has now just changed what 'proper' is.
 