rkehs

New member
i am looking at article 300.3 letter C. my question is can i run 120v along with 24 volt in the same conduit as long as the insulation rating is 300v ??

please help

rkehs
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
At the bottom of 300.3(C)(1) there's an FPN. Check out what Article 725 has to say about it.