spa bonding outside

Status
Not open for further replies.

bkubat1

Member
I Need A Better Understanding Of 680-42b Exception

Q: Can A Outside Portable Self Contained Spa Use A Bonding Grid
Made From Bonding All Motors Pumps & Equip Inside Spa
And Connect Bond To Area Metalic Objects Like Gutters And
Faucets And Just Float Or Must It Be Bonded To The Disc Or
To The Service.
 

M. D.

Senior Member
I'm not sure I understand the qustion ,but this section does not relieve any of the bonding requirements it gives us permission to use equipment mounted on a common metallic skid or frame, to act as the means for bonding.
680.26 would require a separate bonding conductor to be installed for bonding .
 

bkubat1

Member
thanks for the last reply

I take it as you would still need an equipotential bonding grid installed
bummer
I made a big mistake & poured the concrete
is there any safe way of creating an equivelent grid short of tearing out
the concrete
 

M. D.

Senior Member
The grid only needs to be under the paved walking surface if the hot tub is constructed of non conductive material , it does not need to extend under the tub itself
 

Cavie

Senior Member
Location
SW Florida
bkubat1 said:
thanks for the last reply

I take it as you would still need an equipotential bonding grid installed
bummer
I made a big mistake & poured the concrete
is there any safe way of creating an equivelent grid short of tearing out
the concrete

I'm gonna stick my neck out again. I still have some skin left.

680.40 General.

Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this artical. Equipotential bonding is in Part II therefore bonding grid is not required for portabel spa. IMHO.
 

M. D.

Senior Member
680.42. A spa or hot tub installed outdoors shall comply with the provisions of part I and II ...
 