    Load Bank

    We currently rent our load banks for generator testing. We have come to the point where we rent so often that if would pay for us to have our own. I am looking to build a 250kva bank and am looking for wiring diagrams.

  2. #2
    Join Date
    Aug 2004
    Posts
    11,716
    Quote Originally Posted by zeilzabob
    We currently rent our load banks for generator testing. We have come to the point where we rent so often that if would pay for us to have our own. I am looking to build a 250kva bank and am looking for wiring diagrams.
    There is a lot more to a load bank then wiring diagrams.

    There are any number of companies that make them, including the one I work for.

    There are lots of issues that need to be addressed.

    1) water or air cooled?
    2) resistive, inductive, capacitive, or combo?
    3) voltage
    4) load steps
    5) do you need automatic sequencing of loads?
    6) single phase, 3 phase, or combo?
    7) safety issues
    8) monitoring and data collection
    Bob

  3. #3
    Join Date
    Jul 2006
    Location
    Ohio
    Posts
    153
    If your requirements fit into one of their standard designs, Avtron Manufacturing in Cleveland OH may be able to provide you a cost-effective solution. http://www.avtron.com/load_banks.htm

  4. #4
    Join Date
    Jan 2004
    Location
    Right here.
    Posts
    12,326
    You could wire hundreds of hair dryers in a large box.

  5. #5
    Join Date
    May 2003
    Location
    Leesburg, VA
    Posts
    6,933
    I have used load banks for a long time and went through the I can build stage. ONE WORD


    BUY, safe, fast to obtain Try Cannon Load Baks, Avtron or Simplex
    Brian John
    Leesburg, VA

  6. #6
    Join Date
    Aug 2006
    Posts
    13
    The brand I've seen the most at facilities using 200KW+ generators use Avtron load banks.

  7. #7
    Join Date
    Jun 2004
    Location
    San Francisco, CA
    Posts
    5,465
    2500, 100 watt light bulbs....
    Electric heretic
    It's always gonna be in the last place you look....

  8. #8
    Join Date
    Jun 2006
    Location
    The "Live Free or Die" State
    Posts
    508

    If I Really Wanted to Build One

    If I were going to build one, as the original poster is interested in doing, then I would consider paralleling Electric Unit Heaters, such as are found in the Grainger catalog, Stock Numbers 3UF75 through 3UF98. They range in size from 3 KW to 50 KW and include the heat exchangers and fans to get rid of the heat.

    Different sizes could be selected to get a wide range of loads. Just switch in the ones you need to make the load.