JD, welcome to the forum!
For manual disconnecting, a handle tie is adequate, so two or three 1-pole breakers may be joined with a handle tie for multiple line-to-neutral loads.
For automatic operation, as in over-current tripping, an internal common trip is required, so a "real" 3-pole breaker is required for a line-to-line load.