Results 1 to 5 of 5
Thread: L1 & L2 nomenclature
  1. #1
    In a split phase residential panel I am accustomed to seeing the legs named L1 and L2.
    I had always assumed that the L stood for leg.
    Occasionally I see 220V devices that label power connections as L1, L2 and N.
    Occasionally I see 120V devices that label the neutral terminal as L2.
    Is this proper?
    In what situations is it proper to use L1 and L2 as labels?
    Would it be proper to use it on the secondary of a low voltage transformer?
  2. #2
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,767
    L = Line
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,021
    Quote Originally Posted by johnny watt
    L usually stands for Line. Thus L1 and L2
    This is a 220 device with a neutral connection
    Is this proper?
    I have seen it and I don't like it but I am not sure if it is proper. Neutral should be called N for Neutral
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,540
    Is this proper?
    Yes, and quite common. Most 2 wire devices do not care which leg is connected to neutral.
    Any time you have 2 wires supplying power. Unless one of them comes off the third leg of a 3-phase system.
    I don't think I have seen that.
    Bob
  5. #5
    Join Date
    Feb 2003
    Fl
    Posts
    17,095
    Is this proper?
    Actually it is, both conductors connected to the device are current carrying conductors whether the L2 conductor is grounded or ungrounded.
    Roger
Posting Permissions
  • You may not post replies
  • You may not edit your posts