Xfrm. In ceiling space Sec. OCPD

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
When a transformer is located above a suspended ceiling (45Kva) can the secondary OCPD be located in the ceiling space adjacet to the xfmr.? Or does it have to be located below the ceiling?
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
When a transformer is located above a suspended ceiling (45Kva) can the secondary OCPD be located in the ceiling space adjacet to the xfmr.? Or does it have to be located below the ceiling?

IMHO, i would say look at 240.24
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I think that per 240.24(A)(3) and 225.40, the secondary OCPD could be above the ceiling if it supplied (for instance) a branch circuit panelboard that was mounted in a readily accessible location.
 