I seem to have found an incorrect answer to a question in Mike Holts Illustrated Guide to NEC Exam Preparation 2008
Unit 5, Table 5 question asks: What is the cross sectional area for one 1/0 XHHW Compact Conductor?
The Answer given as correct is [c] 0.2733 sq in?
Referring to Chpt 9, Table 5A (Compact Copper & Aluminum Wire Nominal Dimensions and Area) I find the answer to be 0.1352.
Answer [c] is the cross sectional area of one 4/0 XHHW Compact Conductor.
Can someone show me the error of my ways?