LarryFine said:
I don't see your point. :-?
Larry, look at the sentence structure, not so much what it's saying:
(1) Cord-and-Plug-Connected Equipment Not Fastened
in Place. The rating of any one cord-and-plug-connected
utilization equipment not fastened in place shall not exceed
80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires (lighting fixtures), shall not exceed 50 percent of
the branch-circuit ampere rating where lighting units, cord-and-
plug-connected utilization equipment not fastened in
place, or both, are also supplied.
Isn't that a lot of doublespeak if the red phrases and the green phrases are synonymous?
That tells me there is such a thing as cord-and-plug-connected equipment fastened in place, right? GDO's, disposals, microwaves, dryers, and so forth.
Larry Fine said:
Each dryer would be below the 80% limit.
Right, but the pair together would exceed the BC rating, which is prohibited in 210.23 (initial section), IMO.