Thread: Splicing In Residential Service Panels?

  1. #1
    Join Date
    Apr 2007
    Posts
    2

    Splicing In Residential Service Panels?

    Does the NEC allow splicing of wires inside a residential service panel? If yes, are there rules to follow. Can I combine two branch circuits in the service panel to make one circuit, thus freeing up a circuit breaker?

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,420
    Quote Originally Posted by sailor5
    Does the NEC allow splicing of wires inside a residential service panel? If yes, are there rules to follow. Can I combine two branch circuits in the service panel to make one circuit, thus freeing up a circuit breaker?
    Yes you can, nowhere in the NEC does it say that you cannot splice in a panelboard.

  3. #3
    Join Date
    Feb 2005
    Location
    NJ
    Posts
    9,324
    Quote Originally Posted by sailor5
    Can I combine two branch circuits in the service panel to make one circuit, thus freeing up a circuit breaker?
    Which 2?

    By the time you run around checking everything, a tandem CB might cost less.
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    ««« CELTIC »»»
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    An error on your part does not constitute an emergency on my part.8-)


  4. #4
    Join Date
    Apr 2007
    Posts
    2
    A tandom CB cannot be used in this panel.

  5. #5
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,024
    There are rules in the NEC regarding splicing in panels.

    The rules for splicing in any panel can be found in 312.8 2005 NEC. Be sure to read the entire section.

  6. #6
    Join Date
    Feb 2005
    Location
    NJ
    Posts
    9,324
    Quote Originally Posted by sailor5
    A tandom CB cannot be used in this panel.
    Then you better figure what 2 loads you are combining ...aka, more time...aka, more money....and possibly an unhappy customer when all is said is done:
    "I used to be able to have the curling iron on in the bedroom and vacuum in the hallway with no tripping before sailor5 got here! :mad:"
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    ««« CELTIC »»»
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    An error on your part does not constitute an emergency on my part.8-)


  7. #7
    Join Date
    Feb 2007
    Location
    Maine
    Posts
    159
    As Iwire says. 312.8 with splicing etc. But, IMO if you are joining cicuits together in a panel to a OCPD, you're not using it as a junction box. It would be the same as if in a switch box with multiple feeds.
    Last edited by benmin; 04-04-07 at 06:16 PM.

  8. #8
    Join Date
    Jan 2007
    Location
    Newport, NC
    Posts
    1,881
    I remember the same line of thinking about making a splice in a LB. The word on the street was no. NEC will allow if the condulet is listed. I even seem to remember the question on license exam, if memory serves.:rolleyes:
    Thom

    There is no greater sign of wealth than the ability to throw away food.

  9. #9
    Join Date
    Apr 2007
    Location
    Gasquet, CA
    Posts
    104

    two circuits...

    there are limits to how many receptacles can be on a branch circuit, depending on the ocp.

  10. #10
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,024
    Quote Originally Posted by dab
    there are limits to how many receptacles can be on a branch circuit, depending on the ocp.
    dab, there is no NEC limit to the number of receptacles on a residential branch circuit.

    In other than dwelling units each duplex receptacle counts as 180 VA.