I have a new 200hp 460v motor, premieum efficiency, 226 fla , 1800 rpm, 1.15 SF
PF= 86.7, Code F, (4.67). Distance from breaker to starter 30 feet, distance to motor from starter 5 feet, I know the OL for starter, VD using 350mcm is 0.4 or 0.1%. My question is: will 350mcm 75 degree cable be suitable for this application, taking into consideration the inrush-current? Breaker is 600amp frame with 300 amp trip.
PF= 86.7, Code F, (4.67). Distance from breaker to starter 30 feet, distance to motor from starter 5 feet, I know the OL for starter, VD using 350mcm is 0.4 or 0.1%. My question is: will 350mcm 75 degree cable be suitable for this application, taking into consideration the inrush-current? Breaker is 600amp frame with 300 amp trip.