    I need to give a price on a 400 amp, 3 phase 4 wire service, and I don't want to get burned by the derating issue. I was planning on running 4 500mcms in a 4" pvc pipe, the pipe will be about 100' long above a drop ceiling in a retail area. I know by having 4 current carrying conductors I need to derate, but I am not sure how to go about this, any help is appreciated.

  2. #2
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,940
    Are you needing all 400 amps?
    Norb
    My Boss is a Tyrant and my Employee is an Idiot.

  3. #3
    Join Date
    Jul 2005
    Location
    Upper Jay, NY
    Posts
    2,079
    Quote Originally Posted by millspgh
    I need to give a price on a 400 amp, 3 phase 4 wire service, and I don't want to get burned by the derating issue. I was planning on running 4 500mcms in a 4" pvc pipe, the pipe will be about 100' long above a drop ceiling in a retail area. I know by having 4 current carrying conductors I need to derate, but I am not sure how to go about this, any help is appreciated.
    It seems way too far for service conductors considered inside the building envelope. If you end up with feeders, will you need to include an equipment grounding conductor in the conduit as well? :-?

  4. #4
    Join Date
    May 2007
    Posts
    9

    service

    I know I will need an equipment ground also. I am sure th store will not need all 400 amps, but the panel will be a 400 amp main breaker panel

  5. #5
    Join Date
    May 2007
    Posts
    9

    service

    Also, this is coming from an outdoor fused disconnect on the outside of the building, which is fed from an outdoor trough that is fed from a 1200 amp switch outside.

  6. #6
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,940

    310.16...

    Quote Originally Posted by millspgh
    I know I will need an equipment ground also. I am sure th store will not need all 400 amps, but the panel will be a 400 amp main breaker panel
    Correct me if I'm wrong but according to Table 310.16 -- 500 CU is only rated at 380 amps at 70 deg.
    Norb
    My Boss is a Tyrant and my Employee is an Idiot.

  7. #7
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,177
    millspgh, I think you're confusing Feeders and Services. You should read 310.15(B) for whether the neutral will need to be counted as a Current Carrying Conductor.


    Roger
    Last edited by roger; 05-07-07 at 06:54 PM.
    Moderator

  8. #8
    Join Date
    Aug 2006
    Location
    Miami Fla.
    Posts
    6,887
    Mills, are you designing this or bidding from plans?

  9. #9
    Join Date
    Jul 2005
    Location
    Upper Jay, NY
    Posts
    2,079
    Quote Originally Posted by 1793
    Correct me if I'm wrong but according to Table 310.16 -- 500 CU is only rated at 380 amps at 70 deg.
    Would 240.4(B) allow him the next standard rating?

  10. #10
    Join Date
    May 2007
    Posts
    9
    There are no blue prints, the owner of the shopping plaza asked me to give him a price on putting a 400 amp panel in a location a Family Dollar is moving into, fed from the outside of the building at a 4oo amp fused disconnect switch