a 16.75 kw rated range has a full load current value of ? amp for load calculation purposes.
M money mike New member May 10, 2011 #1 a 16.75 kw rated range has a full load current value of ? amp for load calculation purposes.
roger Moderator Staff member Location Fl Occupation Retired Electrician May 10, 2011 #2 See 220.55, read the notes below the table and try to calculate this on your own, show us your method and we can help you from there. Roger
See 220.55, read the notes below the table and try to calculate this on your own, show us your method and we can help you from there. Roger
kingpb Senior Member Location SE USA as far as you can go Occupation Engineer, Registered May 10, 2011 #3 Mike, you would need to know voltage to calculate current.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 10, 2011 #4 Table 220.55 applies if it is a residential range ... Is this a residence calculation?
roger Moderator Staff member Location Fl Occupation Retired Electrician May 10, 2011 #5 Dennis Alwon said: Table 220.55 applies if it is a residential range ... Is this a residence calculation? Click to expand... Good point Dennis, I was assuming, (I know what that leads to :grin if it is other than a residential range see 220.56. Roger
Dennis Alwon said: Table 220.55 applies if it is a residential range ... Is this a residence calculation? Click to expand... Good point Dennis, I was assuming, (I know what that leads to :grin if it is other than a residential range see 220.56. Roger