Results 1 to 3 of 3
Thread: Spacing For Copper Busbars
  1. #1
    engineers,
    what is the minimum spacing for copper busbar assembly
    where in NEC can i find it?
    thanks
  2. #2
    Join Date
    May 2004
    MA
    Posts
    1,472
    Spacing from what??
    Other bussor metal parts???
    try 408.56
    Charlie
  3. #3
    Join Date
    Oct 2005
    Las Vegas, NV
    Posts
    19
    Assuming you are talking about 480V assembly in switchgear, the recent manufacturer I worked for used insulated standoffs that were about 1" thick. The nominal clearance in air we used between uninsulated bus bar and a ground plane was 1" at 480V. When this clearance was not achievable, we would use a phenolic insulating material or insulating fiberboard such as Tufnol.
    See page 26, product on center of page on the following link.
    http://www.bowitt.com/insulating-par...t_Catalog.pdf/
    Ever stop to think, and forget to start again?