Air Compressor Voltage Rating

Status
Not open for further replies.

Bobhook149

Senior Member
Looked at a job today where a new air compressor is to be installed. On the name plate it lists the motor as 3 phase 200v 29A. This seems to be a strange input voltage to me. The voltage in this building is 120/208, do I need to transform the voltage down?
 

hurk27

Senior Member
Looked at a job today where a new air compressor is to be installed. On the name plate it lists the motor as 3 phase 200v 29A. This seems to be a strange input voltage to me. The voltage in this building is 120/208, do I need to transform the voltage down?

No, 200 volt motors are the correct voltage for a 208 volt system, high torque motor applications such as air compressors require the voltage rating of the motor to be close to the supplied voltage, a 230 volt motor in most cases like this would be over loaded.
 

hurk27

Senior Member
Motors are usually rated 208-230. 200v label on motors aren't that common. Is it a Japanese motor?

200 volt motors are very common on 208 systems, Iwire has a chart that show this, and if you call any motor manufacture you will find using a 230 volt rated motor on a 208 system will require derating of the motor, a 10 hp 230 volt motor will only be rated about 7.5 hp at 208, a big problem with air compressors that require a lot of torque to start up, I have seen a few motors on air compressors burn up trying to run a 230 volt motor at 208.

Remember less voltage will cause more pole slippage and more current in a AC motor, so while over voltage is bad, but not as bad as less voltage.
 

hurk27

Senior Member
I'm borrowing Iwires chart that shows what I was talking about:

ANSIC841.jpg


If you look under "nominal" and find 208 follow over to "name plate/motors" you will see 200 volts.

Manufactures can list what ever acceptable voltage their motor will run on, but if you dig deeper you will find most will have either a 200 volt 208 volts only or a 220 volt rating to cover operating from 208 to 240 volts, but if a motor has a straight 230 volt rating, it has to be de-ratted to operate on 208 if it is even allowed.
 
Last edited:

Electric-Light

Senior Member
Aren't they usually rated 208-230 volt or 230 volt?

Yep they are, however many Japanese motors are rated 200v right on the tag, which is the nominal voltage there for a voltage a notch above standard plug-in stuff, which is 100v there.

200v just happens to work real good with our 208v.
 

iwire

Moderator
Staff member
Location
Massachusetts
200v just happens to work real good with our 208v.

No, a NEMA 200 volt motor is designed with the intention of connection to a 208 volt source, just like a 230 motor is intended for connection to a 240 source and a 460 motor is intended for connection to a 480 volt source.
 