Nietz001

Member
Location
St Paul MN
I know in a commercial kitchen area I need all 125 volts rec's to have GFCI protection. Does anyone know if a 208 single phase rec intended for a cord connection also need to be GFCI protected? If so I assume my only option is a 2 pole GFCI breaker.
 

Nietz001

Member
Location
St Paul MN
OK

OK

I did read this and still had some question, it is my understanding that I do not need to protect the 208 rec with GFCI protection.
Thanks
 

Nietz001

Member
Location
St Paul MN
Defense

Defense

I know it's not a valid defense but in a recent arc flash training class the speaker (Electrical Engineer, lots of experience) told me directly if a 208 volt piece of eq is cord and plug connected (in a commercial kitchen) it needed to be GFCI protected. If it's hard wired it's OK. ....Just saying
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I know it's not a valid defense but in a recent arc flash training class the speaker (Electrical Engineer, lots of experience) told me directly if a 208 volt piece of eq is cord and plug connected (in a commercial kitchen) it needed to be GFCI protected. If it's hard wired it's OK. ....Just saying

He be incorrect. :happyno:
 