    Does someone have the formula to determine the amps of 240 volt heat elements connected to a 208 volt system?
    240 volt 10 kw HS = 42 amps
    What are the amps at 208 volts?
    Thanks!!!
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,855
    [quote=Sparky5150]Does someone have the formula to determine the amps of 240 volt heat elements connected to a 208 volt system?
    [quote]
    Ohms Law for constant R
    V1 = I1 X R which can be changed to V1/I1 = R
    V2 = I2 X R and V2/I2 = R
    This means V1/I1 = V2/I2
    Further manipulation gives
    I2 = I1 x V2/V1
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    May 2003
    Maryland
    Posts
    1,527
    You need to determine the resistance of the heater.
    E/I=R
    240/42 = 5.7 ohms
    Now we can figure amperage at 208 volts since E/R=I.
    208/5.7 = 36.5 amps.
    Now instead of 10KW the heater will provide
    208 X 36.5 amps = 7592 watts (7.6 KW).
    Hope that helps.
  4. #4
    Perfect!
    Thanks guys!!!
  5. #5
    Join Date
    May 2007
    Portland
    Posts
    4
    I would check with the heater mfr- most heating elements (actually most metals) have positive CTR so they are non-linear. The current may actually be higher than the simple analysis suggests.
  6. #6
    Join Date
    Sep 2006
    Michigan
    Posts
    457
    What about P = V^2 / R
    P = 240V^2 / 5.76 ohms = 10,000W
    P = 208V^2 / 5.76 ohms = 7,511W
    Then
    I = 7,511W / 208V = 36.1A
    This would mean the heater only has about 75% of the heating capacity at 208V.
  7. #7
    Join Date
    Jun 2005
    Delmarva, USA
    Posts
    1,645
    Arrow
    When the resistance is fixed such as is the case here with heating elements, you don't have to calculate its value. All you need are the 2 different voltages involved, and the known number of rated Watts.
    We can determine the Amps at 240 Volts by taking 10,000/240 = 41.67
    Next, set up a proportion equation thus:
    240 Volts = 41.67 Amps
    208 Volts = (x) Amps
    Solve for (x)
    208 times 41.67 = 240(x)
    8667.36/240 = (x)
    36.11 = (x)
    A loose rule of thumb is the watts will be 75% value at 208 Volts, VS 240 Volts, as shown in other calculations in this thread.
    The reduction of the Amps will be proportional to the change in Volts, in this case 86.7%
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,983
    Another rule of thumb, if you double the voltage you will get 4X the output in watts.
    Rob
  9. #9
    Join Date
    Feb 2003
    Illinois
    Posts
    23,544
    Yes, the watts change with the square of the change in voltage. 208 is 86.6% of 240 and 86.6%^2 is 75.1%.
    Don
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  10. #10
    Join Date
    Jul 2007
    Tampa Florida
    Posts
    39
    I dont want to seem difficult but; None of the formuli shown here to date have taken account of the reduced element temperature.
    The original post didn't say what type of element, a water heater element may not have a very great temperature difference being held somewhat constant by (near) water contact but there will be a larger temperature difference if it is a duct heater.
    The result of the lower voltage will be a decreased temperature and a decreased resistance ; thus increased wattage, depending on the element type used.
    I would feel safer in saying the new calculated amp draw is a MINIMUM.