Steam Shower...

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I'm working on a bathroom and the HO is installing an Ariel Steam Shower. I have no idea what the electrical requirements are.

I have found the unit on-line and the following is the description under the "Specifications" tab:

"Quick Electrical Specifications:
Power Type: 110V, 60 Hz
Max Power Usage: 55+ amps
Breaker Required: Dual-Pole 30 amp GFCI
Wire Required: #10-2 Gauge"

I think something was "lost in translation". :eek:hmy:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have done a few and the largest I did was 50 amps and the smallest 30 amp. Depends on the size of the shower. There definitely seems like something is amiss in the specs.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
Talked with Tech Support and they say this unit is 120V and a 30A GFI is required. The total Amps is with the Pump and Steam system running at the same time. I have had to run the 10/2 and install the 30A in addition to the circuits I have already installed. :eek:
 