Receptacle as required lighting outlet?

Status
Not open for further replies.

frizbeedog

Senior Member
Location
Oregon
210.70 (A) (2) (a)

In a detached garage can the required lighting outlet be a receptacle?

Picture a ceiling mounted recep for a plug in fixture to be installed by joe homeowner after I'm done and gone.

Thoughts please.
 

peter d

Senior Member
Location
New England
I take a "lighting outlet" to be just that, a lighting outlet, not a receptacle. There would be no need for the exceptions in 210.70(a)(1) if lighting outlets included receptacles in the broad definition.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the definition of a lighting outlet:

Lighting Outlet. An outlet intended for the direct connection of a lampholder or luminaire


Do you think that a switch controlled receptacle meets the definition?
 

iwire

Moderator
Staff member
Location
Massachusetts
Jim W in Tampa said:
It is an outlet.Code does not say fixture.

The requirement is not for just an outlet, it is a requirement for a lighting outlet.

Now if you don't want to put a fixture on it I am fine with that. :smile:
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
iwire said:
The requirement is not for just an outlet, it is a requirement for a lighting outlet.

Now if you don't want to put a fixture on it I am fine with that. :smile:

So Bob,would you pass it with the receptacl in ceiling that is switched?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Jim W in Tampa said:
So Bob,would you pass it with the receptacl in ceiling that is switched?


A switched receptacle is permitted for the connection of a HID fixture. One could argue that a switched receptacle for a cord and plug connected low bay lighting fixture would meet the requirement.
 

frizbeedog

Senior Member
Location
Oregon
infinity said:
A switched receptacle is permitted for the connection of a HID fixture. One could argue that a switched receptacle for a cord and plug connected low bay lighting fixture would meet the requirement.

Because of the HID lighting with receps scenario, I keep asking myself the question.

Also: Is a plug a direct connection as used in the definition of a lighting outlet?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
georgestolz said:
The key to the definition is "direct connection," not "cord and plug connection."


So a garage with a low bay HID light plugged into a switch control receptacle wouldn't satisfy the lighting out requirement for a detached garage?
 

Buck Parrish

Senior Member
Location
NC & IN
Just thought I would through this in. 2008 code says if both top and botton of a duplex outlet is switched then it does not count as a required outlet.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
buckofdurham said:
Just thought I would through this in. 2008 code says if both top and botton of a duplex outlet is switched then it does not count as a required outlet.

I believe that George actually made that proposal.
 

frizbeedog

Senior Member
Location
Oregon
quogueelectric said:
Why not just put in a keyless porcelain with a recepacle built in and call it a day. GFCI protected of course.

Funny you should mention GFCI protection on the receptacle in the ceiling. I often install a recep for a GDO and now you have me thinking I should have been providing GFCI protection for these all this time. 210.8 (A) (2) seems to confirm that. I see no exception. :)
 

iwire

Moderator
Staff member
Location
Massachusetts
electricalperson said:
a lot of older homes around here have a switched receptacle in the bedroom and no celing lighting outlets

That is still allowed in many rooms, but not the garage.

Exception 1 of 210.70(A)(1)
 

iwire

Moderator
Staff member
Location
Massachusetts
quogueelectric said:
Why not just put in a keyless porcelain with a receptacle built in and call it a day.

Not sure if that is OK.

Take a look at 410.47.

'Lampholders of the screw shell type shall be installed for use as lamp holders only'
 