    Question Smoke EVAC system
    Can you explain what added components (to a fire alarm system) are typically needed for a smoke EVAC system and the typical type of application that would require the use of a smoke EVAC system.
    Thanks!!
    Keri :grin: :grin:
  2. #2
    Join Date
    Jul 2006
    Cape Coral, Fl.
    Posts
    299
    Typically I've seen smoke evac for atrium's in hotels.
    It requires a central DDC system to open dampers, operate specific AHU fans, and specific exhaust fans.
    It is fairly involved and site specific. i would get in touch with my local NICET level II or III fire alarm contractor for help.
    Living in the sunshine, staying contented most of the time.
  3. #3
    Join Date
    Aug 2007
    MN
    Posts
    143
    Evac
    Be careful when bidding and check with the Local Fire Marshall.
    Most EVAC systems require that the Fire Alarm cabling be installed in conduit. Depending on the Buildign and the reason for the smoke EVAC, you may need to pressurize the stairwells and the floor above and floor below the floor of fire.
    If it is for Warehouse smoke evac then the wiring may be required to be MI or installed "outside" of the structure.
    Just two cents from the Fire Marshalls I have run across.
  4. #4
    Join Date
    Sep 2006
    Michigan
    Posts
    457
    Where I have seen it required was any atrium which is 3 or more floors in height. (I think it might be an IBC requirement) I've seen exceptions when the floors above the second floor were enclosed in a fire rated glass assembly. Smoke evacuation systems are complicated and from what I read on it they need to be modeled in some 3d software for proper sizing and design. There was also a requirement for a dedicated fire figher command room with direct access to the outside.
  5. #5
    Join Date
    Jun 2003
    Posts
    6,836
    There are two types of systems the IBC may require. One is a "smoke and heat" vent, and the other is basically a smoke evac (i can't remember exactly what the IBC calls this one.) The smoke evac is easier to comply with. Its basically some big fans with a switch for the fire dept. to use. Atriums that connect 3 floors is one example where these are required.
    The "smoke and heat vents" are more stringent. They may need emergency back up power, fire resistant wiring methods and even a fire command center. I think these are more typical in high rise applications.
    Steve
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    I think there are as many answers as there are buildings and designers. :smile:
    I have hooked up some very simple ones and some very complicated ones. Some that the FACP controlled entirely others that the FACP signaled a building management system. One I did in a large dept store could pressurize or evac depending on the fires location using 4 large dedicated smoke evac fans and 15 HVAC roof top units.
    Most have some sort of override / manual controls available for the fire dept.