Results 1 to 6 of 6
Thread: Texas residential code and breaker box location
  1. #1
    Texas requires compliance with the NEC that was in effect May 1, 2001. First, what version was of the code was effective at that time. Second, is there any requirement in it that conflicts with the following legislation:
    Section 2306.514 is amended to provide that each breaker box must be located not higher than 48 inches above the floor on the first floor of each single family home constructed with funds from TDHCA, unless the applicable building code prescribes another location.
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,939
    I can't speak to your first question. But the only related NEC requirement of which I am aware places a limit on the maximum height of 6 feet (i.e., to the highest overcurrent device). This is in 240.24. Since the legislative action you cite places a lower limit on the maximum height, it is not in conflict with the NEC requirement.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    8,309
    My guess is that the NEC in enforcement at that time would have been the 1999.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  4. #4
    Loacation of Breaker Boxes - Inside or Outside?
    Does the NEC have any requirement concerning the location of the breaker boxes? Does it specify inside or outside the dwelling or not mention any specific location at all. Can you please provide me with the cite concerning the box location? Thanks.
  5. #5
    Join Date
    Aug 2007
    Broward Co.
    Posts
    361
    try 408.37 -> 312.2 (A)
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by Ralph Hendrickson
    You can put a panel board most anywhere inside or outside a dwelling other then a closet or a bathroom.
Posting Permissions
  • You may not post replies