    I'm planning on using a Line Isolation Monitor panel in an OR, (Cardiac cath lab actually) The way I read the code these LIMS are required. I'd also like to put both normal and emergency power.

    Of course Square D makes a dual LIM panel that probably anticipates this purpose.

    Now, I have three CATH labs side by side. Can I install two LIM panels, one emergency one normal, and serve three labs? Or is there some limit for distance of wiring (Impedance is specifically adressed in NFPA 99) or a grounding issue that will prevent me from using two LIMs for three suites? I might have to go 50 feet or more to get from one lab to another.

    Each suite is required to have a LIM monitoring panel in plain sight. Do they make remote LIM monitors? Can you put three remote monitors on one LIM, for three suites?

    Thanks!
    Lawrence Lile, P.E.

  2. #2
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,062
    Quote Originally Posted by lile001
    I'm planning on using a Line Isolation Monitor panel in an OR, (Cardiac cath lab actually) The way I read the code these LIMS are required. I'd also like to put both normal and emergency power.

    Isolation Power Systems are optional per the NEC. They are required in certain areas such as NC. Both Normal and Critical branches are required in these rooms though.

    Quote Originally Posted by lile001
    Of course Square D makes a dual LIM panel that probably anticipates this purpose.
    These dual panels are nice, we use alot of them

    Quote Originally Posted by lile001
    Now, I have three CATH labs side by side. Can I install two LIM panels, one emergency one normal, and serve three labs? Or is there some limit for distance of wiring (Impedance is specifically adressed in NFPA 99) or a grounding issue that will prevent me from using two LIMs for three suites? I might have to go 50 feet or more to get from one lab to another.
    You will find that the combined leakage of numerous conductors will add up fast, SQ D will not commission a panel that has more than .0005 Amps of leakage in an idle state. Actually .0006 (200,000 ohms) is the cut off but SQ D uses .0005.

    Quote Originally Posted by lile001
    Each suite is required to have a LIM monitoring panel in plain sight. Do they make remote LIM monitors? Can you put three remote monitors on one LIM, for three suites?
    Yes, they make remote Line Isolation Monitors and you can put as many as neccessary downstram of the panel, you will most likely need the ones with the milliammeter.


    Roger
    Moderator

  3. #3
    Join Date
    Jun 2003
    Posts
    5,559
    Check NFPA 99 13.4.1.2.6.5: An isolation transformer shall not serve more than one operating room except....

    The exception is basically for Xray and HV equipment.

    I'm not sure if your cath lab would be considered an operating room.


    Edit: After rereading your post, you're not asking what I though you were. I'm not sure if you planed on having separate isoltion panels or not.

    Steve
    Last edited by steve66; 08-30-07 at 04:20 PM.

  4. #4
    Join Date
    Sep 2004
    Location
    Midwest
    Posts
    154
    Quote Originally Posted by steve66
    Check NFPA 99 13.4.1.2.6.5: An isolation transformer shall not serve more than one operating room except....

    The exception is basically for Xray and HV equipment.

    I'm not sure if your cath lab would be considered an operating room.


    Edit: After rereading your post, you're not asking what I though you were. I'm not sure if you planed on having separate isoltion panels or not.

    Steve
    Thanks! That was the code section I needed. NFPA 99 is the code that requires LIMs in operating rooms, NEC just makes them optional. The thinking is, operating rooms can be wet locations, but you don't ant GFI's tripping circuits during an operation, so the isolation transformer makes a single fault to ground not dangerous.

    These CATH labs are definitely operating rooms, according to the surgeons. Your Mileage May Vary at your institution, it depends on how the surgeons intend to use the space. So it looks like we must have a dual LIM panel in EACH operating room suite. YOW! No wonder my insurance bill is going up!
    Lawrence Lile, P.E.

  5. #5
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,062
    Lile, NFPA 99 does not require Isolated Power Systems any more than the NEC does. The applicable sections of where they are permitted to be used are NFPA 99 4.3.2.2.9 and 4.3.2.2.10.

    Roger
    Moderator

  6. #6
    Join Date
    Sep 2004
    Location
    Midwest
    Posts
    154

    LIM Panels

    Correct, niether NFPA 99 nor NEC requires LIM panels, they are optional. In my case they are required by the facility. The facility has also determined that these labs will be surgery areas, and could be wet locations, thus the LIM panels are a good idea.



    I do want to find a code reference that requires both normal and emergency power in this kind of area. NEC refers to "patient bed locations" as needing two flavors of power. I am not sure that a "patient bed location" is the same as a surgery room. Is there a code reference that anyone else can find that requires both normal and emergency power in a surgery suite? Or can someone present an argument of sublte sophistry that can make the case that this is a "patient bed location"?
    Lawrence Lile, P.E.

  7. #7
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,062
    It's in the definitions.

    Patient Bed Location. The location of an inpatient sleeping bed; or the bed or procedure table used in a critical patient care area.
    Patient Care Area.

    Critical Care Areas. Those special care units, intensive care units, coronary care units, angiography laboratories, cardiac catheterization laboratories, delivery rooms, operating rooms, and similar areas in which patients are intended to be subjected to invasive procedures and connected to line-operated, electromedical devices.
    Roger
    Moderator

  8. #8
    Join Date
    Nov 2005
    Location
    Canterbury, New Zealand
    Posts
    1,877
    Its still not clear what your intention is for "two panels" and "three labs"; I would opine that each lab should have its LIM(s) serving it, as any other arrangement would be a nightmare for the staff should the alarm sound.

  9. #9
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,062
    Quote Originally Posted by dbuckley
    Its still not clear what your intention is for "two panels" and "three labs"; I would opine that each lab should have its LIM(s) serving it, as any other arrangement would be a nightmare for the staff should the alarm sound.
    I agree, if trying to use these panels for more than one room you would need to locate them in a sterile corridor common to all the rooms, remote LIM's and milliammeters for each branch would be needed within each room.

    Roger
    Moderator

  10. #10
    Join Date
    Jun 2003
    Posts
    5,559
    Quote Originally Posted by lile001
    So it looks like we must have a dual LIM panel in EACH operating room suite. YOW! No wonder my insurance bill is going up!
    You can say that again:smile:

    I wish the code would be a little more definate on if isolation panels are required. Engineers usually don't know enough about the procedures preformed to decide if they are necessary. And trying to get anyone in the facility to make that call is usually a dead end.

    It seems like one of those danged if you do, and danged if you don't things.

    Steve