![]() I have done similar installations and to tell the truth never gave it much thought but,.. would the structure to the right (post with required receptacle outlet) require a disconnect ? I think it meets the definition of a "structure" and as such would require one . I also think it is an outbuilding as described in the exception to 225.36. Next question ;does the snap switch have to be at or near the structure served? I think it does In the area where I work this would not be tagged as a 225.31 violation. Has anyone ever been tagged for this? stories and Opinions Please.
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#2
|
||||
|
||||
|
Wow! that is some back yard. In the area I am from, there would probably be about a 1000 homes in that picture.
From what I can see by your photo, the receptacle would be premitted as your disconnecting means. Nice picture..."a picture is worth a thousand words."
__________________
Instructor, Industry Advocate |
|
#3
|
||||
|
||||
|
Thanks for the reply Pierre, I'm not sure the receptacle provides a disconnecting means as to disconnect the ungrounded conductors that supply the structure though
If this structure were a garden shed with a receptacle installed would it not require a disconnect??
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
|
#4
|
||||
|
||||
|
I think the NEC requires a disconnecting means.
A while back I installed four 30 amp 208 volt branch circuits to receptacles on a single post at a fair grounds. Once the job was underway and I really started to think about it I think I was in violation of 225.30 225.31 250.32(A) In the end the inspector felt it was fine as it was.
__________________
Bob |
|
#5
|
||||
|
||||
|
Quote:
225.30 in the case of this post, there seems to be only one circuit per post 225.31 The receptacle could be the disconnecting means 250.32(A) The exception to (A) would most likely suffice here, meaning no grounding electrode would be required by NEC.
__________________
Instructor, Industry Advocate |
|
#6
|
||||
|
||||
|
Quote:
Do you have receptacles rated as service equipment per 225.36? Do you have any receptacles that meet the requirements of 225.38? In my opinion the receptacle in the picture can serve as the disconnecting means for the pump but by the letter of the code it can not serve as the disconnecting means for this 'structure'.
__________________
Bob |
|
#7
|
||||
|
||||
|
Quote:
__________________
4 Out Of 3 People Have Trouble With Fractions The National Sarcasm Society Like We Really Need Your Support |
|
#8
|
|||
|
|||
|
Read through 680 for Storable Pools. How deep is the pool (see definition of a storable pool)? 680.7, 680.12 for disconnecting means. 680.21(A)(1)&(5) minimum equipment gound and length of cord, 680.22(A)(5) GFCI within 10', 680.22(A)(1,2,3,4) for pump 5' to 10' from pool and 680.26(B) for equipotential bonding.
Last edited by RAYMFL; 09-21-2007 at 05:23 PM. |
|
#9
|
||||
|
||||
|
Quote:
It is a matter of the NEC defining that post the receptacle is on as a structure.
__________________
Bob |
|
#10
|
||||
|
||||
|
Quote:
It does seem "stupid" for a post to require a disconnect but if you read Bob's first post in this thread ,it seems a little less so. It is funny to me that most, if not all of us ,would agree that a garden shed with a receptacle outlet installed would require a disconnect ,is there really a difference between the shed and the post in regard to the the disconnect and why it is required??? I think perhaps an exception for residential property might be a good idea.
__________________
"America will never be destroyed from the outside. If we falter and lose our freedoms, it will be because we destroyed ourselves." Abraham Lincoln |
![]() |