Default Spot the violation(s)

We built this today despite a violation I told the owner about. He said the AHJ wont catch it.
There is 1 more violation you might not catch.

DSCN0376small.jpg
  #2  
Old 09-22-2007, 05:22 PM
peter d's Avatar
peter d peter d is offline
Senior Member
 
Join Date: Mar 2003
Posts: 10,170
Default

Are those 3R disconnects? They look like they are but I can't really tell.
  #3  
Old 09-22-2007, 05:23 PM
peter d's Avatar
peter d peter d is offline
Senior Member
 
Join Date: Mar 2003
Posts: 10,170
Default

As for the "hidden" violation, are there service and feeder conductors sharing that trough?
  #4  
Old 09-22-2007, 05:23 PM
360Youth's Avatar
360Youth 360Youth is offline
Senior Member
 
Join Date: Jan 2007
Location: Newport, NC
Posts: 1,730
Default

Trough sticking out too far in front of discs?? You gots me under pressure, man! I can't take it!!!

I can't tell if your strapping is good on the 2", if that is the vague violation you speak of.
__________________
Thom

Music may be timeless, but performers are not.
  #5  
Old 09-22-2007, 05:27 PM
chris kennedy's Avatar
chris kennedy chris kennedy is offline
Senior Member
 
Join Date: Aug 2006
Location: Miami Fla.
Posts: 5,621
Default

Quote:
Originally Posted by 360Youth
Trough sticking out too far in front of discs?? You gots me under pressure, man! I can't take it!!!
Thats it. And those are 4". Not the strapping.
  #6  
Old 09-22-2007, 05:34 PM
roger's Avatar
roger roger is offline
Moderator
 
Join Date: Feb 2003
Location: N.C.
Posts: 12,155
Default

If that gutter is not more than 6" out past the disconnects (it doesn't appear to be) there is no violation.

Roger
__________________
Moderator

Last edited by roger; 09-22-2007 at 05:39 PM.
  #7  
Old 09-22-2007, 05:39 PM
infinity's Avatar
infinity infinity is offline
Moderator
 
Join Date: Jul 2003
Location: New Jersey
Posts: 12,476
Default

Quote:
Originally Posted by roger
If that gutter is not more than 6" out past the disconnects (they don't appear to be) there is no violation.

Roger
I agree, it looks like a 12" wireway, if the front of the disco's is more than 6" off the wall to the front no violation of article 110 exists.
__________________
Rob

Moderator
  #8  
Old 09-22-2007, 05:42 PM
chris kennedy's Avatar
chris kennedy chris kennedy is offline
Senior Member
 
Join Date: Aug 2006
Location: Miami Fla.
Posts: 5,621
Default

Quote:
Originally Posted by roger
If that gutter is not more than 6" out past the disconnects (they don't appear to be) there is no violation.

Roger
See the 9" kliens. The gutter is 10" from the front of the discos. I read the owner of my company 110.26(A) (3) and he said he never heard of it so the inspector won't know.

The other violation is 366.6(A). That gutter was built by a sheet metal shop down the street.
  #9  
Old 09-22-2007, 05:47 PM
roger's Avatar
roger roger is offline
Moderator
 
Join Date: Feb 2003
Location: N.C.
Posts: 12,155
Default

Quote:
Originally Posted by chris kennedy
See the 9" kliens. The gutter is 10" from the front of the discos. I read the owner of my company 110.26(A) (3) and he said he never heard of it so the inspector won't know.
Actually those look more like 3" toy pliers.

Quote:
Originally Posted by chris kennedy
The other violation is 366.6(A). That gutter was built by a sheet metal shop down the street.
And how were the members supposed to see or know that?

(BTW, the sheet metal shop probably turned out an equal in quality piece of equipment as any commercialy sold NEMA 3 gutter)

Roger
__________________
Moderator
  #10  
Old 09-22-2007, 05:51 PM
chris kennedy's Avatar
chris kennedy chris kennedy is offline
Senior Member
 
Join Date: Aug 2006
Location: Miami Fla.
Posts: 5,621
Default

Quote:
Originally Posted by roger
Actually those look more like 3" toy pliers.



And how were the members supposed to see or know that?

(BTW, the sheet metal shop probably turned out an equal in quality piece of equipment as any commercialy sold NEMA 3 gutter)

Roger
I sould have put a man in the pic for perspective. This is a 1600A 3 phase service.

And how were the members supposed to guess the hidden violation?
Because you guys are all knowing.
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 06:46 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.