Beam Pockets

Status
Not open for further replies.

AAEB

Member
Location
Southeast Asia
Good Day!

What is the best alternative to heat detectors in basement parking? We have a recent project in where the beam depth is 700mm and spaced 3500mm center to center???

thanks,
AAEB
 

dhalleron

Senior Member
Location
Louisville, KY
If using the National Fire Alarm Code NFPA 72, each pocket would need to be treated as a separate space if using heat detectors. So probably one heat detector in each pocket depending on ceiling height.

Is there a sprinkler system? If so, then you may not need heat detection.

It's possible they go by a different code in your country.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Good Day!

What is the best alternative to heat detectors in basement parking? We have a recent project in where the beam depth is 700mm and spaced 3500mm center to center???

thanks,
AAEB

If the beam depth is more than 0.1 of the floor to ceiling height, AND the beam spacing is more than 0.4 of the floor to ceiling height, then a detector is required in the pocket. Assuming of course that you are using NFPA 72, 2007 or later.

steve66's suggestion regarding Protectowire or other linear detection product is good. And they are listed for fire alarm.
 