Page 1 of 2 12 LastLast
Results 1 to 10 of 19
Thread: PVC duct bank question.
  1. #1
    Join Date
    Jul 2007
    Texas
    Posts
    648
    (I have already been looking but canít find a reference to this.)
    Question:
    Is there a mandate or a code requirement in NEC 2005 that requires that I put chairs on PVC in a duct bank?
    Specifics
    1. (5) Five feet deep
    2. No concrete
    3. 6Ē sand envelope (bottom, top and sides).
    4. (8) eight 2Ē PVC with 3 phase 480 feeders
    5. Located under building pad.
    Type fast before a mod comes along and shuts down the thread...
  2. #2
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,645
    I can only come up with 310.15(B)(2)(b) & annex B. Annex B has separations from 7.5" to 10" center to center of pipe. Hope this helps.
    Ron
  3. #3
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,436
    I never use them. Here are two 3" and two 2" over four 3". At 480V your 300.5 not 300.50
    Attachment 868
    Sorry about the crappy pic.
  4. #4
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,890
    310.15(B)(2)(b) does require that spacing be maintained. But that is similar to the requirement that for parallel conductors the distances be equal. How equally spaced do they have to be? For my money, if you can find a way to keep the conduits spaced in a reasonably even way through the use of sand or other material, I would be happy.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  5. #5
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,436
    Quote Originally Posted by charlie b
    310.15(B)(2)(b) does require that spacing be maintained. How equally spaced do they have to be?
    I'm thinking more along the lines of what is space. A mm, 4", mabey 10' ?
  6. #6
    Join Date
    Feb 2003
    Illinois
    Posts
    23,470
    I submitted a proposal to specify the minimum space between conduits 3 or 4 code cycles and the panel rejected it with a comment that if you have enough space to install couplings and locknuts you have spacing.
    Don
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  7. #7
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,436
    Quote Originally Posted by don_resqcapt19
    Don
    Well then Don that means the conduits are touching each other. So you should propose that the term raceway is taken out of 310.15(B)2(B).
    BTW what was the min. spacing you had in mind and why? Have you seen an underground failure due to heating?
  8. #8
    Join Date
    Feb 2003
    Illinois
    Posts
    23,470
    Chris,
    No, if the couplings and locknuts are touching, the conduits will have small spaces between them.
    Not sure what spacing I wanted, and the only reason was that the current rule is vague and unenforceable.
    I have not, but there are a number of documented cases where they have, but only when the loads were not calculated using Article 220. These cases were the supporting information for what is now Annex B. At one time those tables were going to be in the actual code rule. They were published in Article 310 with an effective date 3 years later, but moved to the annex in the next code cycle.
    Don
    Don, Illinois
  9. #9
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,436
    Chris,No, if the couplings and locknuts are touching, the conduits will have small spaces between them.
    I beg to differ. Given the inherent flex of RNC conduit I have long runs that are pushed together during backfill. So as far as ITO's OP, we do not worry about or enforce this.
  10. #10
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by chris kennedy
    That may be one way to look at or I might be inclined to say that the spacing of at least the couplings and connectors must be maintained and that because of PVC flexibility we have to provide something to maintain that spacing.
Posting Permissions
  • You may not post replies
  • You may not edit your posts