    And another 2008 question

    Does a metal raceway that penetrates a rooftop vertically and enters directly into the bottom of a disconnect (cutout box) have to comply with the ampacity adjustment rules of (new) section 310.15(B)(2)(c)? If yes, is there any way around derating the conductors?
    Ryan Jackson, Salt Lake City
    Inspector, Instructor

  2. #2
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Quote Originally Posted by ryan_618
    Does a metal raceway that penetrates a rooftop vertically and enters directly into the bottom of a disconnect (cutout box) have to comply with the ampacity adjustment rules of (new) section 310.15(B)(2)(c)? If yes, is there any way around derating the conductors?
    After a quick peak at the change, here is my take.

    Yes, the raceway penetrating the roof and installed in a vertical position will require derating - "installed in conduits exposed to direct sunlight ON or ABOVE rooftops."


    Notice this says CONDUITS and EXPOSED TO DIRECT SUNLIGHT

    I would think they were very specific in this wording.
    If so, then raceways may not be the proper term, but conduits which include...RMC, IMC and RNC. I wonder, by the wording they chose, if they meant to not include EMT-electrical metallic TUBING ?
    What about a trough (wireway) installed in rooftop locations?
    Instructor, Industry Advocate

  3. #3
    Join Date
    Feb 2005
    Location
    NJ
    Posts
    9,324
    Quote Originally Posted by Pierre C Belarge
    I wonder, by the wording they chose, if they meant to not include EMT-electrical metallic TUBING ?
    What about a trough (wireway) installed in rooftop locations?
    You might want to re-read 100~ Raceway
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    ««« CELTIC »»»
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    An error on your part does not constitute an emergency on my part.8-)


  4. #4
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Conduits are raceways, but not all raceways are conduits...
    Instructor, Industry Advocate

  5. #5
    Join Date
    Feb 2005
    Location
    NJ
    Posts
    9,324
    Maybe I oughta read your question again

    I see what you mean...CONDUITS is the question, not RACEWAYS
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    ««« CELTIC »»»
    ĦĦĦĦĦĦĦĦĦĦĦĦ
    An error on your part does not constitute an emergency on my part.8-)


  6. #6
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,789
    Quote Originally Posted by Pierre C Belarge
    if they meant to not include EMT-electrical metallic TUBING ?
    What about a trough (wireway) installed in rooftop locations?
    I cannot imagine why EMT would be excluded from this derating. I would assume that the derating has to do with the heat that is produced from the rooftops thus incresing the ambient temp.

    I would guess that masts for services would also be affected.

  7. #7
    Join Date
    May 2003
    Location
    Salt Lake City, Utah
    Posts
    5,319
    What about the part that says "bottom of conduit". Does that mean it only applies to horizontal raceways?
    Ryan Jackson, Salt Lake City
    Inspector, Instructor

  8. #8
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Ryan
    I read the wording out of the analysis book. I do not see where it says the "bottom" of the conduit. It the wording different in the actual code book?
    Instructor, Industry Advocate

  9. #9
    Join Date
    May 2003
    Location
    Salt Lake City, Utah
    Posts
    5,319
    I don't have my code book here, but I am pretty sure that the table is measured to the "bottom" of the conduit.