qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Just finished a detached residential garage with its own service.
Had everything on G.F.I except garage door openers and 1 receptacle in the upstairs (finished storage) for the required outlet at the HVAC.
Inspector came back and had me put them on G.F.I.
Was he correct to require the G.F.I's?
What is the code article? We just went to 2008.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The inspector was correct. 210.8(A)(2) just says "garages," without any exceptions for specific loads or areas within garages.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
The inspector was correct. 210.8(A)(2) just says "garages," without any exceptions for specific loads or areas within garages.

Thanks Charlie!
Thought maybe it being detached might get me something.
Can call it a day! Learned something!
 