    A customer just installed two, used, Overhead Door openers on his shop building. The motor control is "old school" and I am drawing a blank. The up/down/stop control has a 5 conductor cable to it. I figured out 3 of them.
    Up and Down have a N.O. contact, and the stop has a N.C.
    I can make the up/down work, but not the stop. The customer thinks that UP should be pressed once and the contact on the opener should hold until the limit switch is made. But, right now, UP or DOWN have to be held the whole time. (Release and the motor stops). I believe it is because I don't have the STOP wired in properly.
    On the Diagram:
    UP = C31 - C4
    Down = LS4 - C4
    Any help?
    My son is one of the Few, the Proud, the Infidel.
    Sgt. Mickey, 0311 USMC
  2. #2
    Join Date
    Mar 2006
    close to greenville sc
    Posts
    1,020
    I'm having a hard time with the drawing. I can't find any way that the LS's would hold in the contacts. Maybe because I stayed too long at the VFW last night! Many of the industrial overhead doors are designed so that someone has to keep the buttons pushed in to avoid accidents. The limit switches are to keep someone from going up or down too far.
    Military wives deserve the Purple Heart Medal. They are wounded every time their Soldier goes off to protect our freedom!
  3. #3
    Join Date
    Jul 2006
    Posts
    2,571
    Same here. Most, if not all, of the roll-up doors I've seen will only move when the button is held. The stop button seems redundant.
  4. #4
    Join Date
    Jan 2006
    Cocoa, Florida, USA
    Posts
    318
    Wink
    Think I would go directly to the fountainhead . . .
    www.overheaddoor.com
    You may even find the guy who drew up that confusing 1991 drawing.
    Best Wishes
    Steve
    Be Safe Out There
  5. #5
    Join Date
    Nov 2007
    East of 480sparky
    Posts
    1,121
    it looks to me as if e1 thru e2 should control the coils for up and down and the c's should be the holding contacts, just a guess. LS's should open the holding contacts..............again, just a guess:-?
  6. #6
    Join Date
    Oct 2007
    Maryland
    Posts
    295
    overhead door
    all the overhead door we have on site require you to hold the up and down button to keep it moving. We have a couple that are older and will maintain contacts and go out on limits. They have problally been modified though with an extra relay.
  7. #7
    Join Date
    Dec 2005
    The Sooner Nation
    Posts
    2,437
    I did not get a chance to go by there today.
    http://overheaddoor.com was NO HELP at all!
    The limit switches must be connected internally on the board though, as they are part of the circuit. Customer is adamant that the Up be momentary - held by contacts.
  8. #8
    Join Date
    Oct 2007
    British Columbia, Canada
    Posts
    816
    It's difficult to figure out without seeing how the rest of the terminal block is wired.
    This is my first time trying to draw ladder logic in ASCII...
    Momentary to open and close:
    Code:
    <--- [/]STOP ---+---+--- []UP ---+--- [/]LS-UP --- (/)DN --- ()UP --->
                    |   +--- ()UP ---+
                    +---+--- []DN ---+--- [/]LS-DN --- (/)UP --- ()DN --->
                        +--- ()DN ---+
    From this I'd suggest wiring the terminal block as such:
    Connect C2 and C4
    Connect C31 and LS3
    Connect LS2 and E2
    Connect C32 and LS4
    Connect LS1 and E1
    Connect the Stop switch between C and C2/C4
    Connect the Up switch between C2/C4 and C31
    Connect the Down switch between C2/C4 and C32
    I'm working on the assumption that LS2/LS3 is fully open and LS1/LS4 is fully closed,
    and that the guy who designed this used those stubby golf-ball sized crayons.
    "The Doppler effect means red lights will appear to be green if you drive fast enough..."
    1) Wait for disaster 2) Determine it's not your fault 3) Blackmail the culprit 4) Profit
    Caution: Classless when exhausted from a tough day at work, may attempt to compensate with poor humor and Christmas cheer...
  9. #9
    Join Date
    Dec 2005
    The Sooner Nation
    Posts
    2,437
    Hey, thanks Rick!
    Yes, I would think the designer rode to school on the short bus.
  10. #10
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,830
    The OHDs I've installed will go up without being held, but not down... that must be held in.