Does a walk-in gen-set must meet NEC working space requirement.?
Doesn't matter. It's a UL listed assembly. The NEC stops at the door to the equipment. Same goes for walk in RTU's and prefabricated telco buildings.QES said:Does a walk-in gen-set must meet NEC working space requirement.?
QES said:See an code problem with this panel?
ryan_618 said:I disagree that it isn't within the scope of the NEC. I inspected a UL listed building that needed two exits and only had one. I failed it, notified UL, and they applauded me for it. They then visited the site where they are manufactured and re-evaluated the buildings.
Depending on what your going to vent... ?QES said:See any code problem with this panel?
sandsnow said:Contrary to popular belief, UL does not knowingly allow products with Code violations to be listed or classified.
iwire said:We sure could go round on that. :smile:
Look at a typical residential dishwasher, does the open wiring on the bottom comply with the rules in the NEC?