    Romex in PVC pipe ?

    Hi , I'm hoping that I can get help in this forum. a few questions that I have are.
    can I pull Romex 14-2 in a 1/2" PVC pipe that goes underground?
    do I need 2 grounding electrodes at the meter?.
    well , any help will be really apreciated.

    thank you very much

  2. #2
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,211
    Quote Originally Posted by ronaldsax
    Hi , I'm hoping that I can get help in this forum. a few questions that I have are.
    can I pull Romex 14-2 in a 1/2" PVC pipe that goes underground?
    No, you can not pull NM in an underground conduit, you can use UF though.


    Quote Originally Posted by ronaldsax
    do I need 2 grounding electrodes at the meter?.
    well , any help will be really apreciated.
    thank you very much
    If a rod type GE is the sole GE and you don't want to prove 25 ohms or less, the answer is yes.

    Roger
    Moderator

  3. #3
    Join Date
    Nov 2007
    Location
    Massachusetts
    Posts
    76
    No, you can not pull NM in an underground conduit, you can use UF though.

    can you give an article number, I'm trying to find it thanks

  4. #4
    Join Date
    Sep 2004
    Posts
    1,465
    334.12(B) NM not permitted in damp or wet areas.
    Article 100: Location, wet: Installations under ground.
    300.5(B) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.