Results 1 to 5 of 5
Thread: Romex in PVC pipe ?
  1. #1
    Romex in PVC pipe ?
    Hi , I'm hoping that I can get help in this forum. a few questions that I have are.
    can I pull Romex 14-2 in a 1/2" PVC pipe that goes underground?
    do I need 2 grounding electrodes at the meter?.
    well , any help will be really apreciated.
    thank you very much
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    16,876
    Quote Originally Posted by ronaldsax
    No, you can not pull NM in an underground conduit, you can use UF though.
    thank you very much
    If a rod type GE is the sole GE and you don't want to prove 25 ohms or less, the answer is yes.
    Roger
    Join Date
    Nov 2007
    Massachusetts
    Posts
    76
    can you give an article number, I'm trying to find it thanks
  4. #4
    Join Date
    Sep 2004
    Posts
    1,497
    334.12(B) NM not permitted in damp or wet areas.
    Article 100: Location, wet: Installations under ground.
    300.5(B) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.
    Mark
    Kent, WA
  5. #5
    Join Date
    Nov 2007
    Massachusetts
    Posts
    76
    thanks for the reply
Posting Permissions
  • You may not post replies
  • You may not edit your posts