Not if it falls under NEC 210.8 (A)(7)76nemo said:Is the 6' rule gone now in the last 5-6 years?
resistance said:Not if it falls under NEC 210.8 (A)(7)
dining area of a restraunt
nizak said:Would GFCI protection be required for countertop 120V receptacles that are located above food prep tables in a dining area of a restraunt? How about if they are within 3 or so feet of a sink?
6" or 60' is irrelevant...what is relevant is the bold portion above...special attention to the underlined words.2005 NEC said:210.8(B)(2) Commercial and institutional kitchens—for the purposes of this section, a kitchen is an area with a sink and permanent facilities for food preparation and cooking