310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.
Dennis Alwon said:I would be careful on this one. The op is asking about a solid bare conductor.
In this case you would still run the EGC in the PVC back to the CT can to bond it.iwire said:But do you need an EGC?
Utility > CT > service disconnect > switchboards
chris kennedy said:In this case you would still run the EGC in the PVC back to the CT can to bond it.
Why? There is no need for an EGC until you get to the load side of the service disconnect. You use the grounded conductor for all required line side bonding.chris kennedy said:In this case you would still run the EGC in the PVC back to the CT can to bond it.