Can you run a bare solid ECG conductor inside a PVC conduit with 4 insulated
wires? This is also service conductors from CT cabinet to switchboards. Any
imput would help Thanks.
 

iwire

Moderator
Staff member
Location
Massachusetts
Yes you can run bare.

But do you need an EGC?

Where is the service disconnecting means?

Utility > CT > service disconnect > switchboards

OR

Utility > service disconnect > CT > switchboards
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would be careful on this one. The op is asking about a solid bare conductor.

310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
iwire said:
But do you need an EGC?
Utility > CT > service disconnect > switchboards
In this case you would still run the EGC in the PVC back to the CT can to bond it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
chris kennedy said:
In this case you would still run the EGC in the PVC back to the CT can to bond it.


If the bonding jumper was at the disconnect why would you need an EGC from the CT to the disconnect? The grounded conductor would be bonded to the CT can.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
chris kennedy said:
In this case you would still run the EGC in the PVC back to the CT can to bond it.
Why? There is no need for an EGC until you get to the load side of the service disconnect. You use the grounded conductor for all required line side bonding.
 