Page 1 of 3 123 LastLast
Results 1 to 10 of 27
Thread: Voltage Drop vs distance chart available?
  1. #1
    Join Date
    Jan 2008
    South Carolina
    Posts
    685
    I am wondering if there is a chart of some sort available that will give me wire size needed for varying amperages at a given distance. I am working in a warehouse and am hoping to avoid running alot of caculations. For example I need to place a 30A/240V receptacles at 250 from the panel. Then another at 230 feet and so on. Just hoping there may be a premade answer out there.
    Thanks,
    c2500
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    There on line calculators available, I doubt you will find a chart as there are to many variables.
    A rough method is to bump up a size per 100'
  3. #3
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,836
    Are these receps on the same circuit? And will they both be used at the same time? And what is the actual amperage draw [load] on the circuit (not the recep. rating)?
  4. #4
    Join Date
    Jan 2008
    South Carolina
    Posts
    685
    Each recptacle will be on an individual circuit. I would have to guess the max draw would be 24amps.
    c2500
  5. #5
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,441
    IMO voltage drop calcs are a worst case scenario. I fired up parking lot lights yesterday and my calcs said I would have 196V at the last 208V fixture. I have 204V there? Go figure.
    This is not the first time I have noticed this.
  6. #6
    Join Date
    Apr 2007
    Posts
    658
    did you use the Zoltek 99 wireguide?
  7. #7
    Join Date
    Feb 2003
    Alabama
    Posts
    2,668
    Quote Originally Posted by chris kennedy
    What was the voltage at the main? You may have started with 215 volts
    instead of 208 volts.
  8. #8
    Join Date
    Jun 2004
    San Francisco, CA
    Posts
    5,468
    Many variables like starting actual voltage vs. nominal, actual load vs. name-plate, load distributed along the cicruit vs. at the end, etc.
    source>>>>>>>middle>>>>>>>>end
    208>>>>>>>>>>>>>>>>>>>>total load 196
    208>>load>>>load>>>load>>>load>>>Last 204
    Volts 208 207 206 205
    Less load>>>>>>>>>>>>>>>>>>>>>Higher load
    Electric heretic
    It's always gonna be in the last place you look....
  9. #9
    Smile Fast way to do voltage drop
    I don't know of any voltage drop charts but if you have to do a lot of voltage drop calculations then you might as well buy Electric Calc Pro. It is a very nice $100 dollar calculator that solves the voltage drop really easy and much more.
  10. #10
    Join Date
    Jun 2007
    Ogdensburg, NY
    Posts
    2,257
    Talking That'd be nice.
    Quote- Just hoping there may be a premade answer out there.
    Don't we all:grin: It doesn't hurt to dream.
    Old and in the Way.......
Posting Permissions
  • You may not post replies
  • You may not edit your posts