Isolated Ground Retrofit

Status
Not open for further replies.

slo7682

Member
If an existing 208/120V electrical system served from a 480V to 208/120V transformer has an equipment ground conductor with all feeder and branch circuit conductors but does not have an isolated ground conductor, and needs one, can an isolated ground conductor be added in a separate conduit outside of the system circuit conductors? If so or if not, by what part the NEC.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It cannot be run in a raceway or cable that does also contain the circuit conductors. 250.146(D) and 300.3(B)
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
slo7682 said:
If an existing 208/120V electrical system served from a 480V to 208/120V transformer has an equipment ground conductor with all feeder and branch circuit conductors but does not have an isolated ground conductor, and needs one, can an isolated ground conductor be added in a separate conduit outside of the system circuit conductors? If so or if not, by what part the NEC.

You can add one there, but it can't be the only EGC for that circuit,as the EGC has to be run with the circuit conductors.
 

crossman

Senior Member
Location
Southeast Texas
If you want to add some IG receptacles, or change existing receptacles to IG receptacles, the IG Equipment Grounding Conductor will need to comply with 250.146(D). This section will require the conductor to be run with the circuit conductors.
 