Thread: Any body bond or ground the gas meter

  1. #1
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,051

    Arrow Any body bond or ground the gas meter

    Does the 2008 NEC require that we bond or ground the gas meter in a sfd.

  2. #2
    Join Date
    Jan 2004
    Location
    Right here.
    Posts
    12,326
    I don't. Matter of fact, the gas company in my area claims that will mess up their cathodic protection system. I don't know if that's true or not.

  3. #3
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,051
    Whats a cathodic protection system?

  4. #4
    Join Date
    Nov 2007
    Location
    massachusetts
    Posts
    3,166
    its ok to bond gas pipe but you cant use it as a GEC. local codes might be different. i dont bond the gas pipe.

  5. #5
    Join Date
    Aug 2006
    Location
    Miami Fla.
    Posts
    6,905
    Quote Originally Posted by buckofdurham
    Does the 2008 NEC require that we bond or ground the gas meter in a sfd.
    Won't it be bonded through the EGC of the appliances?

    Second to last sentence of 250.104(B)

  6. #6
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,051

    Angry

    I'm wiring a house in Chatam County NC, I,m told the inspections require you to run a seperate ground from the main panel all the way to the meter. This house has a 400 amp service and the gas meter is on the other side of the house.

  7. #7
    Join Date
    Nov 2007
    Location
    massachusetts
    Posts
    3,166
    Quote Originally Posted by chris kennedy
    Won't it be bonded through the EGC of the appliances?

    Second to last sentence of 250.104(B)
    thats how its bonded. but i dont physically run a conductor and bond it to the service.

  8. #8
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    I believe part of the issue in regards to bonding of gas pipes today has developed due to CSST (corrugated stainless steel tubing - the flexible gas piping - Gastite, Wardflex, etc...). The manufacturers have their own installation instructions that go beyond the NEC requirement of 250.104(B).

    NYS has put together a committee to deal with the situation, and if I am not mistaken, the state wide code will be amended to deal with the issue, plumbing and electrical.

    I can also say that one of the methods of dealing with this in NYS may ultimately lead to the banning of CSST installations in the state.
    I will let you guys know when I hear...I have been invited to sit at the meetings.
    Instructor, Industry Advocate

  9. #9
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,450
    Quote Originally Posted by buckofdurham
    I'm wiring a house in Chatam County NC, I,m told the inspections require you to run a seperate ground from the main panel all the way to the meter. This house has a 400 amp service and the gas meter is on the other side of the house.
    I work in chatham county , NC also-- you are talking about CSST or gastite gas lines. Yes you must bond that back to the panel.

    Edit: I guess I should have read Pierre's statement first.

    Be careful in Chatham I have had them tell me to bond the CSST pipe with a #4 to the ground rod. This, of course, is not what the manufacturer states. Unfortunately I cannot get an installation instruction that is consistent. I refuse to bond them now. I tell the gas people, you install it , then you bond it. I do not want the liability.
    Last edited by Dennis Alwon; 01-20-08 at 01:40 PM.

  10. #10
    Join Date
    Jul 2007
    Location
    Mooresville NC
    Posts
    22
    In Manalapan NJ. we run a number 2 copper to gas meter if the water pipe is plastic. Even if we have a CEE we still have to do it.