Results 1 to 5 of 5
Thread: Installing ground rods?
  1. #1
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,507
    I've just ran power to 10 new irrigation center pivots. I drove all rods vertically but talking to the other guys, they said they've just buried them before. 250.53(G) 05 code, the way I'm interpreting it says I can't bury them unless rock is encountered when driven, is this correct? The ditch next to the pivot is open making it effortless to bury them. Do they actually enforce this in your area? Thanks.
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,019
    Quote Originally Posted by Cow
    I agree with you.
    Art. 250.53(G) is pretty clear
    (G) Rod and Pipe Electrodes. The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,507
    Thanks Dennis.
  4. #4
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    Ground rods actually work better (the little work they do) when installed horizontally in the ground about 2' deep...
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  5. #5
    Join Date
    Jun 2004
    San Francisco, CA
    Posts
    5,468
    You dont have to drive a plate....
    Electric heretic
    It's always gonna be in the last place you look....