Above dropped ceiling in commercial building:ohmy: Code ref. please. Thanks in advance:)
H Hendrix Senior Member Location New England Aug 13, 2012 #1 Above dropped ceiling in commercial buildinghmy: Code ref. please. Thanks in advance
rcarroll Senior Member Location Fort Collins, Colorado Aug 13, 2012 #2 Not allowed. 338.10(4)(a) then 334.12(A)(2)
kwired Electron manager Location NE Nebraska Aug 13, 2012 #3 rcarroll said: Not allowed. 338.10(4)(a) then 334.12(A)(2) Click to expand... To clarify a little 338.10(4)(a) tells us when used for interior wiring SE cable shall comply with part II of art 334, and 334.12(A)(2) is what doesn't allow it.
rcarroll said: Not allowed. 338.10(4)(a) then 334.12(A)(2) Click to expand... To clarify a little 338.10(4)(a) tells us when used for interior wiring SE cable shall comply with part II of art 334, and 334.12(A)(2) is what doesn't allow it.