Closed Thread
Page 1 of 6 1 2 3 ... LastLast
Results 1 to 10 of 52
Thread: Running Romex in conduit
  1. #1
    I'm doing some electrical work at this electronic manufacturing facility. I noticed that whoever did the electric before me ran 12-2 Romex in 1/2" EMT. Does this meet code. I didn't think Romex in conduit was to code. If not why? Is it a heat related thing?
  2. #2
    Join Date
    Jul 2007
    Iowegia
    Posts
    16,614
    Quote Originally Posted by horrorsix
    NM is allowed in pipe, but it usually isn't done because of fill issues. That, and theres no rainbow of colors available.
  3. #3
    Join Date
    Feb 2006
    Lake of the Ozarks
    Posts
    2,722
    Quote Originally Posted by 480sparky
    Thhn you use the 90C table for Amp rating romex you use the 60C table
  4. #4
    Join Date
    Feb 2003
    N.C.
    Posts
    14,621
    It's perfectly fine.
    See any of the 3xx.22 sections, for example 358.22
    358.22 Number of Conductors
    The number of conductors shall not exceed that permitted by the percentage fill specified in Table 1, Chapter 9.
    Cables shall be permitted to be installed where such use is not prohibited by the respective cable articles. The number of cables shall not exceed the allowable percentage fill specified in Table 1, Chapter 9.
    Roger
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    23,539
    Quote Originally Posted by roger
    Roger
    Hey Roger
    Do you have the chart that had been posted with the dimensions of nm. I would guess that 12 nm will be overfill for 1/2" emt. Just a guess.
    I also bet a residential guy did that job. :grin:
  6. #6
    Join Date
    Feb 2003
    N.C.
    Posts
    14,621
    Quote Originally Posted by Dennis Alwon
    Hey Roger
    Dennis I don't have the chart but I do remember it
    Very possibly the case. :wink:
    Roger
    Join Date
    Jul 2006
    California
    Posts
    254
    ever try pulling romex in 1/2" conduit??? NOT FUN.
    Got a Ph.D in DIY...
  8. #8
    Join Date
    Mar 2003
    New England
    Posts
    10,398
    Quote Originally Posted by QES
    One run of 14/2 or 12/2 is not that difficult.
  9. #9
    Join Date
    Jan 2004
    Right here.
    Posts
    12,327
    14-2 NMB .1018
    12-2 NMB .1320
    10-2 NMB .1917
    8-2 NMB .2942
    6-2 NMB .3664
    14-3 NMB .0740
    12-3 NMB .0946
    10-3 NMB .1399
    8-3 NMB .2507
    6-3 NMB .3318
    14-2 UF .1405
    12-2 UF .1684
    10-2 UF .2107
    8-2 UF .3610
    6-2 UF .4657
    14-3 UF .2651
    12-3 UF .3078
    10-3 UF .4151
    8-3 UF .8808
    6-3 UF 1.1747
    Don't forget that it's 53% for one cable.
  10. #10
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    4,896
    Quote Originally Posted by mdshunk
    14-2 NMB .1018
    12-2 NMB .1320
    10-2 NMB .1917
    8-2 NMB .2942
    6-2 NMB .3664
    14-3 NMB .0740
    12-3 NMB .0946
    10-3 NMB .1399
    8-3 NMB .2507
    6-3 NMB .3318
    14-2 UF .1405
    12-2 UF .1684
    10-2 UF .2107
    8-2 UF .3610
    6-2 UF .4657
    14-3 UF .2651
    12-3 UF .3078
    10-3 UF .4151
    8-3 UF .8808
    6-3 UF 1.1747
    What type of dimensions are these? Noticed that 14-2 is greater than 14-3. As is 12
    Tom
    TBLO
Closed Thread
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts