COMMENT 13-14 445.17 <except> in text as 11-14

Status
Not open for further replies.

fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 13-14. Thanks, Jim Williams

4 Comment:
revise this text as follows:

red is deleted

445.17 Generator Terminal Housings. Generator terminal housings shall comply with 430.12. Where a horsepower rating is required to determine the required minimum size of the generator terminal housing, the full-load current of the generator shall be compared with comparable motors in Table 430.247 through Table 430.250. The higher horsepower rating of Table 430.247 and Table 430.250
shall be used whenever the generator selection is between two ratings.

Exception: This section shall not apply to generators rated over 600 1000 volts. [ROP 11?14 13-14]


5 Statement of Problem and Substantiation.

430 has the dividing line reset to 1000v rather than 600v. Since this references 430 it should have the same dividing line.
 